    OK that makes sense for that diagram

    I had another question on the same diagram. I am referring to the potential relay part of the diagram. On the diagram when the 5-2 coils is energized it drops out the start capacitor. That part makes sense. The part I do not understand is the start winding goes to herm on the dual cap and then to common out to terminal 23 on the contractor. To me it looks like the start winding is never dropped out but the start cap is. Basically when I follow the the start winding it goes com>start>herm>com>23. How is the start winding dropped out.

    Thanks again

  2. #15
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,960
    Post Likes
    Quote Originally Posted by Noname81 View Post
    OK that makes sense for that diagram

    I had another question on the same diagram. I am referring to the potential relay part of the diagram. On the diagram when the 5-2 coils is energized it drops out the start capacitor. That part makes sense. The part I do not understand is the start winding goes to herm on the dual cap and then to common out to terminal 23 on the contractor. To me it looks like the start winding is never dropped out but the start cap is. Basically when I follow the the start winding it goes com>start>herm>com>23. How is the start winding dropped out.

    Thanks again
    The *ST (Start Thermistor) or PTC (Positive Temperature Coefficient Thermistor), can be used in place of the *SR (Start Relay) and *SC (Start Capacitor).

    Both are not used together as the wiring diagram shows. It is just showing you how each would be wired, if installed.
    Instead of learning the tricks of the trade, learn the trade.

  3. #16
    Join Date
    May 2003
    Location
    Charleston SC
    Posts
    150
    Post Likes
    they are not in parallel to the compressor contactor-they are in series. When one of the safeties opens, the logic in CTD opens that switch. It is pictured as normally open but its actually normally closed and locks out to prevent short cycling.
    Regards Coolairman

  4. #17
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,657
    Post Likes
    Quote Originally Posted by rundawg View Post
    The *ST (Start Thermistor) or PTC (Positive Temperature Coefficient Thermistor), can be used in place of the *SR (Start Relay) and *SC (Start Capacitor).

    Both are not used together as the wiring diagram shows. It is just showing you how each would be wired, if installed.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.