Results 1 to 9 of 9
Thread: Voyager
    Jul 2018
    Wisconsin
    Voyager
    What will cause a RTRM diagnostic fault With no fault on the ignition board? Its Intermittently doing it only in heat. If any limits trip Ignition board is first in line.
    Sent from my SM-G920R4 using Tapatalk
    Dec 2014
    I think TC01, TC02?
    Sent from my SM-G930V using Tapatalk
    Jul 2018
    Wisconsin
    That will throw a fault on the ignition board. I physically removed spade from the limit while it was running and it faulted the ignition board and the rtrm board.
    Jul 2018
    Wisconsin
    I swaped boards with the unit next to it. We will see if the problem follows the board.
  5. Likes icy78 liked this post
  6. #5
    Dec 2014
    Just sitting here eating lunch and I'm reading about the Voyager heating or I should say , reliatel heating. Says gas heat: if any failure occurs such as loss of flame, limit switch , flame rollout , indicates on the rtrm.
    Further Diagnostics are available by examining the ignition module LED.
    (We have had quite a lot of trouble in the last 3 years with the Emerson ignition board.)
  7. #6
    Jul 2018
    Wisconsin
  8. #7
    May 2014
    Bay Area California
    I had a similar one a couple of months ago. Combustion blower would come on but nothing else. Spent a couple of minutes checking the obvious. Then swapped the heat board with another unit on the same roof. Problem followed the board.
    I consider myself lucky. I'll take it when I can get it, LOL
    I use 56% silver on everything except steel.
  9. #8
    Jul 2018
    Wisconsin
    What would trigger a fault on the rtrm board but not the ignition board when the heat is running? I called tech support but I think the guy was more worried about getting me off the phone and I was freezing my ass off on a windy ass roof.
  10. #9
    May 2014
    Bay Area California
    Not communicating proper?
    There is a Reliatel manual, something shy of 4 meg, which equates to something over 100 pages. Last time I needed it, the check out procedures are pretty thorough. But your conditions might make it more difficult.
    Didn't see an email in your profile.
    Quote Originally Posted by Spitz View Post