    Which Honeywell U module ?

    Which of the Honeywell universal HSI modules will work on a burner without a flame rod? A burner with only HSI sensing for proof of ignition.

    S8910U 1000 maybe?

    If not; which one?
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  2. #2
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    243
    Post Likes
    Was thinking the S8910U 3000 but it looks like it needs a rod. Found A Fenwal that looks like it would work

    Sent from my SM-G920R4 using Tapatalk

  3. #3
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    243
    Post Likes
    Fenwal 35-65 or 35-66

    Sent from my SM-G920R4 using Tapatalk

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,560
    Post Likes
    Keep the black jumper on for local sense
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  5. #5
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    243
    Post Likes
    S8910U 3000 will work for local sense

    Sent from my SM-G920R4 using Tapatalk

  6. #6
    Join Date
    Sep 2002
    Posts
    22,928
    Post Likes
    Thread Starter
    It's a Weil McLain boiler with multiple burners but single point sensing - no flame rod. If I had more time I would add a flame rod and bring it into at least the last century - but I don't.

    What's in there is a Fenwal conversion kit - with a board-edge-plug to terminal converter harness. The problem actually is that the 120V contacts on the original plug are burned and so the ignitor doesn't always get power. But I have no access to Fenwal on a weekend so I wanted to use a HW universal HSI kit.

    I have 5 of them on the shelf in the shop. Every Effin Box is either empty or has an old used control in it. Finding that I was instantly reminded of the day that I fired everyone who worked for me.

    But thanks guys - the 8910U 1000 that I could get from a plumbing house (open until 3:00P) worked out well and I was able to hard wire it to minimize the wiring connections.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.