    I think it's because you can't see it in the exported points table. You can see the fallback value (relinquish default?) in the exported point though. Maybe this is it?



    Scott Jalbert
    WebCTRL ninja
    AX and Smartstruxure newb

    The S in IoT stands for Security

  2. #15
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,079
    Post Likes
    Guessing.

    They don't show the automatic linking of the alarm stuff either, but it happens in the background. Ie, if you have a out of range alarm extension setup on a point that's exported, the alarm high/low values are automatically mapped to the equivalent BACnet properties according to docbacnet.
    Propagating the formula. http://www.noagendashow.com/

  3. #16
    Join Date
    Mar 2018
    Posts
    99
    Post Likes
    I’ve had weird stuff like that happen and sometimes all it took was deleting the proxy point, bringing it back in again.


    Sent from my iPhone using Tapatalk

  4. #17
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,093
    Post Likes
    Thread Starter
    Sorry been busy, if you set a relinquish default value, it automatically writes that value to the point, which when not in use should be --. When that point has a value the user cannot adjust the stat.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  5. #18
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,079
    Post Likes
    Quote Originally Posted by joey791 View Post
    Sorry been busy, if you set a relinquish default value, it automatically writes that value to the point
    That's determined by your tuning policies in most drivers. If its something like a setpoint adjustable in the space, you want to leave max write to zero so it only writes on change. Ie last man wins in that case. Occupants can control it in most cases, but a OWS command can also change it.

    Viconics stat with occupant adjustable setpoint, needs max write set to zero on that point or their change will be overwritten by tbox at some point.

    Write on up/boot/etc also should be false unless you want it to reset it on these conditions.
    Propagating the formula. http://www.noagendashow.com/