    Is it possible to write to a specific slot in the priority array for a BV? If so, how does the syntax statement read?

    Thanks,

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,322
    Post Likes
    From my last experience with Delta (10+ years ago) only physical IO supported priority arrays, values did not. You can look up the PICS of the controller and verify it.

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  3. #3
    Join Date
    Dec 2014
    Location
    Vancouver, BC
    Posts
    37
    Post Likes
    kontrolphreak is correct. In all Delta Controllers v3.40 firmware and older only the physical IO points have priority arrays. So your BV will not have one.

    The new v4.x firmware does have priority arrays for variables as well, but that's a pretty recent addition and only supported on their new stuff so I doubt that's what you've got there.

  4. #4
    Join Date
    Apr 2009
    Location
    chicago
    Posts
    100
    Post Likes
    Actually Delta has supported priority arrays since v3.2, orcaview
    if the hardware supported it, and there was a period were only physical AO BO, objects had it,, and AV n BVs came shortlly after.

    that not being the case then,

    Ifonce object changed then
    BV1.Reset = 1
    BV1.CurrentPriority = 2
    BV1.PriorityArray[2] = 1
    End If