    Oat sensors

    Has anyone ever swapped a carrier oat sensor( 33zcsenoat) with a Honeywell c7089 oat sensor. From the literature I found online they are both at 10k ohm-77’F. It just looks like the carrier is more accurate and has a wider range of temperatures. But the carrier is 4-5 times the price. I just ended up with an extra carrier edge pro(33cs2pp2s-03) that the customer didn’t want so I was looking to use it at home. I’ll be using a heatpump with fossil fuel backup so I’ll need that cutout from the oat. Thanks

  2. #2
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    947
    Post Likes
    Quote Originally Posted by Pres1227 View Post
    Has anyone ever swapped a carrier oat sensor( 33zcsenoat) with a Honeywell c7089 oat sensor. From the literature I found online they are both at 10k ohm-77’F. It just looks like the carrier is more accurate and has a wider range of temperatures. But the carrier is 4-5 times the price. I just ended up with an extra carrier edge pro(33cs2pp2s-03) that the customer didn’t want so I was looking to use it at home. I’ll be using a heatpump with fossil fuel backup so I’ll need that cutout from the oat. Thanks
    are they a match across the entire spectrum instead of just at 77 degrees ?

  3. #3
    Join Date
    Mar 2018
    Location
    Maryland
    Posts
    185
    Post Likes
    Thread Starter
    dang it

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    76,049
    Post Likes
    No they aren't. At 32 OAT the Honeywell is 27,219 ohms, and the Carrier is 32,651 ohms. Which means the Honeywell connected to the Edge would give you an indicated temp somewhere around 39 to 40 degrees F when its 32 outside.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    947
    Post Likes
    Quote Originally Posted by beenthere View Post
    No they aren't. At 32 OAT the Honeywell is 27,219 ohms, and the Carrier is 32,651 ohms. Which means the Honeywell connected to the Edge would give you an indicated temp somewhere around 39 to 40 degrees F when its 32 outside.

    if OP is only using OAT sensor to switch the system over, and OP could care less if the actual OAT is displayed, might be able to adjust temperature to compensate, so long as the OAT sensor does not fall below or above any minimum or maximum ohm readings

    suppose OP could compare the 2 charts and see if the OAT OP experiences are still listed on the OAT sensor

  6. #6
    Join Date
    Mar 2018
    Location
    Maryland
    Posts
    185
    Post Likes
    Thread Starter
    I guess I could just find the corresponding temp and lock out there. Because aslong as it cuts out when I want it to I could care less if the temp reading on the stat is accurate