Results 1 to 5 of 5
  1. #1
    Join Date
    May 2018
    Posts
    6
    Post Likes

    Rack manuals/info

    Do any of you guys have rack manuals or any related material on them? Any info on this particular rack would be great because it is the one I'm working with currently but info on ANY Is greatly appreciated..***Hill Phoenix
    Model# Ps525sMrad***I have a good understanding of the refrigeration cycle and the main components of it (compressor, condenser, metering device, and evaporator). I'm now trying to really dive in on all the different valves in a rack system and ESPICIALLY get a true understanding of the pressures in the system... for example, if I put my gauges on the suction header and it reads 50 psig, how do I figure out if that's the correct pressure? This is the kind of knowledge im still lacking. Thanks for any help in advance fellas I'm looking forward to hearing from u guys..

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,833
    Post Likes
    The manuals are available on line.

    As far as header pressure....Med, Low temp. what % are valves, comp on line........ It all varies and changes.

  3. #3
    Join Date
    Sep 2008
    Location
    Vancouver , BC
    Posts
    411
    Post Likes
    Does this rack have a controller? Check the suction setpoint and use a gauge to verify transducer.
    This is one of the best manuals out there in my opinion
    https://www.hillphoenix.com/tyler/me...ual-lowrez.pdf

  4. #4
    Join Date
    Nov 2018
    Posts
    24
    Post Likes
    Generally rack suction should be low enough to facilitate the coldest case. For example, a R404a rack has multiple cases and the coldest one needs to be -10. The suction pressure at the suction header should be very close to 24Psig. This is an easy way to isolate rack, OR case problems most of the time and allow you to do less running around. Neumonic posted a very good link for a rack manual.

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,633
    Post Likes
    Here are a couple more rack manuals which may prove helpful:

    Hussmann - Parallel Rack Systems (2016)
    https://icemeister.net/backroom/wp-c...Rack_IO_EN.pdf

    Kysor/Warren - Parallel Compressor Refrigeration Units I&O - (1990)
    https://icemeister.net/backroom/wp-c...990-cukw08.pdf