    New here and sorry if this topic has already been covered, but what is protocol on traversing stainless steel duct? Is it an acceptable practice?

    Doing a survey on a hospital and don't have the time to go measure all the lab hoods and phoenix exhaust valves.

  2. #2
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    703
    Post Likes
    I'm not a TAB guy but I don't see any difference. Airflow is airflow. Take your reading in the correct locations and should be no issues.

    What does your contract require you to record? You are in a hospital but don't have time to make sure hoods are safe to work in?

  3. #3
    Join Date
    Nov 2018
    Location
    Lexington KY
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by Push It View Post
    I'm not a TAB guy but I don't see any difference. Airflow is airflow. Take your reading in the correct locations and should be no issues.

    What does your contract require you to record? You are in a hospital but don't have time to make sure hoods are safe to work in?
    Lab hoods / exhaust system works fine. Conducting an overall air flow survey on air handlers, return fans, and exhaust systems.
    The building has a huge negative pressure and the client wants a snapshot of the air systems. I know that stainless steel used for kitchen hood purposes produce high temperature and is thus frowned upon of doing a duct traverse. Not sure if the chemicals used here could potentially pose a problem with drilling holes in the duct.

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Do not drill holes in the kitchen hood unless provisions have been made to have the holes seal welded. The same goes for any duct that carries anything that can be hazardous. If the building is negative you have too much exhaust or not enough outside air.
    To be perfectly honest the hospital should hire a balance contractor.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. Likes BALloyd, heatingman liked this post.
  6. #5
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    My method to figure out negative buildings is very simple and I have used it many times . I start at each exterior door at all four sides of the building to confirm the building is actually negative . Sometimes you can have air going in on one side of the building and air going out on the other side . Especially if the building is not sealed well and it is windy . It can also have air going in one side and out the other due to the different compartments / new wing additions. After confirming the building is negative I just follow the air through the building by closing one set of double doors at a time . Following the air takes you right to the negative area , usually the kitchen . In my opinion measuring all the outside air and exhaust is usually the last thing I would do . Following the air and finding the culprit area is much more effective .

  7. Likes heatingman liked this post.
  8. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by freqdrive View Post
    Lab hoods / exhaust system works fine. Conducting an overall air flow survey on air handlers, return fans, and exhaust systems.
    The building has a huge negative pressure and the client wants a snapshot of the air systems. I know that stainless steel used for kitchen hood purposes produce high temperature and is thus frowned upon of doing a duct traverse. Not sure if the chemicals used here could potentially pose a problem with drilling holes in the duct.
    Hospitals ARE negative pressure by design. The closer you get to the nasty bugs the more negative it gets.


    You need toe a little more specific!

  9. #7
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    I have drilled stainless steel ducts for traversing multiple times . As noted previously , welding the holes is the best way . However , I have use 3/8" boiler plugs to seal the holes . They are a threaded steel body with a high temperature rubber gasket . Also......Hospitals are designed neutral by design here in Florida and that's what the AHCA inspectors want to see . I usually "tweek" the outside air a bit ( after they leave ) to make the building slightly positive just to be safe . A negative building is a disaster with all of the humidity here . The problem with leaving a building neutral is it doesn't take much " drift " from the control systems or dirty filters not changed to swing it to the negative side . Its a case of giving them what they need , not what they think they want .

  10. #8
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Just about every commercial kitchen I see has a negative balance.
    It's always the exhaust is way more then the make-up.

  11. #9
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    All kitchens should be slightly negative , it keeps the odors in the kitchen .

  12. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by bradluke0 View Post
    I have drilled stainless steel ducts for traversing multiple times . As noted previously , welding the holes is the best way . However , I have use 3/8" boiler plugs to seal the holes . They are a threaded steel body with a high temperature rubber gasket . Also......Hospitals are designed neutral by design here in Florida and that's what the AHCA inspectors want to see . I usually "tweek" the outside air a bit ( after they leave ) to make the building slightly positive just to be safe . A negative building is a disaster with all of the humidity here . The problem with leaving a building neutral is it doesn't take much " drift " from the control systems or dirty filters not changed to swing it to the negative side . Its a case of giving them what they need , not what they think they want .
    How does negative pressure create humidity issues?

    DO YOU HAVE DOCUMENTS SUPPORTING YOUR CLAIMS. Neutral!

    I’m sure the local authorities having jurisdiction would love to hear leaving them slightly positive

  13. #11
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by bradluke0 View Post
    All kitchens should be slightly negative , it keeps the odors in the kitchen .
    I'm not talking "slightly" I'm talking BIG difference as in large negative pressure. The kind where it's hard to open the doors.
    I see it all the time probably 75 % .

  14. #12
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    I trace pressure profiles with a cigarette lighter. The cheapest and most accurate tool for that purpose in the world. I have done it so much I can normally estimate the pressure pretty close.
    A school I balanced had a room that got so cold it froze the sprinkler pipes. I told the GC his building was leaking severely above the ceiling and he took offense until he saw the infiltrating air blow my lighter out.
    I have seen more negative buildings than positive ones. Dogs and cats get along better than a negative building with electric reheat.
    No man can be both ignorant and free.
    Thomas Jefferson

  15. #13
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    I trace pressure profiles with a cigarette lighter. The cheapest and most accurate tool for that purpose in the world. I have done it so much I can normally estimate the pressure pretty close.
    A school I balanced had a room that got so cold it froze the sprinkler pipes. I told the GC his building was leaking severely above the ceiling and he took offense until he saw the infiltrating air blow my lighter out.
    I have seen more negative buildings than positive ones. Dogs and cats get along better than a negative building with electric reheat.
    I agree , a lighter is the bomb for chasing pressurization . Also , sticking your nose in a door that's open a few inches works great too . I'm not sure I have seen more negative buildings than positive ones but I have seen a bunch . Dogs and cats also get along better than a negative building and Florida humidity ( great line there Wayne , had to use it ….lol )

  16. #14
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I did some work in a hospital quite some time ago. The HVAC was 100% outside air and the building was slightly positive. I would think a hospital with negative pressure would be a recipe for disaster.


    Quote Originally Posted by pecmsg View Post
    Hospitals ARE negative pressure by design. The closer you get to the nasty bugs the more negative it gets.


    You need toe a little more specific!
    I do a triple evac with nitro to remove non condensables.

  17. Likes Spitz liked this post.
  18. #15
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Use the line at will bradlukeD. I think the difference in the negative buildings we both have seen is location in the country. In Kansas we have some humid days but not like Florida. How often do you see a 78 or 79 F wet bulb? The cooling towers here are designed for 78 WB and some for 79 F. Those WB'S are rare here.
    No man can be both ignorant and free.
    Thomas Jefferson

  19. #16
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Hospitals ARE negative pressure by design. The closer you get to the nasty bugs the more negative it gets.


    You need toe a little more specific!
    Hospital rooms are typically designed to be negative compared to the hallways (to prevent the spread of airborne pathogens), but I think overall they want a very slightly positive building because that ensures the fresh air coming into the building would be conditioned.

    Sent from my Moto Z (2) using Tapatalk

  20. #17
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Hospital room pressures depend on how the room is used. In one case you are trying to prevent the patient from contacting a bug. In another case you are trying to prevent them from infecting others.
    I never saw a negative operating room.
    No man can be both ignorant and free.
    Thomas Jefferson

  21. #18
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    Wayne is correct . I also have never seen a negative operating room ( not on purpose anyway )

  22. #19
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by bradluke0 View Post
    Wayne is correct . I also have never seen a negative operating room ( not on purpose anyway )
    Now that would definitely be a recipe for disaster

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •