    Using a belt tension checker

    I have been using the Browning tension checker similar to this one



    I was wondering the proper way to use it. The scale to set the shaft inches on it looks as if it in is in increments of 10. I have seen a couple manuals that ask you to measure the shaft between rotors and divide that by 64. For most sizes I see that would give you a number smaller than one, which would have you basically be setting the O-ring at the bottom of the checker. This doesn’t seem like it would be very accurate to me or if I am just misunderstanding things.

    Anyways anyone who is more familiar with those things could hopefully clear this up for me. Or if there is another more accurate way to check belt tension I should look into would also be helpful.

  2. #2
    Join Date
    Apr 2007
    Location
    New Brunswick, Canada
    Posts
    259
    Post Likes
    • Measure the center-to-center distances on the shafts. This is your span. Set the large O-ring to this measurement.
    Yes, this is in 10 lb increments, so it can be hard to be dead accurate.

    • Zero the small O-ring.

    • Place the tension checker in the center of the belt and apply force. Stop when it reaches it's original position. Use the adjacent belt as a reference.
    I utilize a ruler or thin angle as a straight edge if it's a single belt.


    I use these all the time. The older guys think I'm crazy. You must have the tension chart for the brand and model of belt that you are using.

    The "divide by 64" you referred to is the ratio of deflection. The belt will push down 1/64" for every inch of span.


    For example: Belt Span = 32"

    32 64 = 1/2" of deflection

    The longer the belt, the greater the deflection.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,398
    Post Likes
    Download the instructions. I use it on every belt driven job.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

    Technically speaking, they are all heat pumps.

  4. #4
    Join Date
    Apr 2018
    Posts
    8
    Post Likes
    Thread Starter
    Thank you very much this was helpful.
    Quote Originally Posted by FrostGiant View Post
    Measure the center-to-center distances on the shafts. This is your span. Set the large O-ring to this measurement.
    Yes, this is in 10 lb increments, so it can be hard to be dead accurate.

    Zero the small O-ring.

    Place the tension checker in the center of the belt and apply force. Stop when it reaches it's original position. Use the adjacent belt as a reference.
    I utilize a ruler or thin angle as a straight edge if it's a single belt.


    I use these all the time. The older guys think I'm crazy. You must have the tension chart for the brand and model of belt that you are using.

    The "divide by 64" you referred to is the ratio of deflection. The belt will push down 1/64" for every inch of span.


    For example: Belt Span = 32"

    32 64 = 1/2" of deflection

    The longer the belt, the greater the deflection.

  5. #5
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    5,722
    Post Likes
    I wouldnt use it on any smaller units, say 5-7.5 tons. Some systems even state right by the blower to only tighten untill blower doesnt squeel on start up. I believe others here could elaborate better on that.


    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    6,539
    Post Likes
    Quote Originally Posted by Core_d View Post
    I wouldnt use it on any smaller units, say 5-7.5 tons. Some systems even state right by the blower to only tighten untill blower doesnt squeel on start up. I believe others here could elaborate better on that.


    Sent from my iPhone using Tapatalk
    I think that it depends on the mounting design of the motor or the plate the motor is on.

    Resilient mount motors move quite a bit when under the same tension you would run standard foot mount.

    And some motor brackets, such as are used by Carrier on smaller units are very flimsy and will bend.


    Sent from my iPhone using Tapatalk

  7. Likes Core_d liked this post
  8. #7
    Join Date
    Nov 2018
    Location
    North Bergen,NJ
    Posts
    8
    Post Likes
    Great info, I didn't even know this tool existed. I'll be getting one for sure as I'm a bit of a perfectionist rather than a good-n-tight type of wrencher.

  9. #8
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,016
    Post Likes
    A discusion on belt tensioning (and alignment), the right or wrong ways of tightening the belt could go on for weeks and months. There is so much more than just getting the tension "right". Go on-line and download the instructions for your tool that will get you a long way toward the good, but not all the way. If you are into the vibration diagnostics you can dial in the best tension and performance.

    But back to belt drives. What is the correct way, the one that provides the correct air flow and last a long time. As a tech/mechanic our job is to deliver an air flow that meets the design requirements for each system and provide the most cost effective and reliable system as we can. There are many factors you have to take into consideration.

    A deflection/tension gauge does two things. 1. It gives you a value to write on the service ticket for the owner or next tech to work on it. 2. By using the tool to let's say make adjustements so you have: 1/2" deflection with 20 pounds of force, you teach yourself just what it takes to get those parameters (experience). There is an art as well as science in setting up belt drives.

    We each have our own method of getting there. As long as you understand what you are trying to achieve and you deliver it, you don't need to follow the recommended values dictated by fan and belt manufactures. (with an explaination)

    Heat is the #1 destroyer of belts, where does the heat come from (process air, bad alignment, too much tension, too little tension, bad design. Bad design meaning: wrong belt size, wrong number of belts, wrong belt type, wrong sheave, wrong bearing type, wrong motor size, wrong fan size, poor designed belt guard just to mention a few. All belt manufacturers agree if you increase the temperature at which the belt operates by 10F you will reduce the service life by 50%. Engineers have been known to get it wrong, the HVAC tech before you might have got it wrong, the homeowner who worked on it last screwed it up, are all possible

    The variable are endless. What is correct is dependent on each drive combination. But the general guidelines for the tension gauges are an excellent place to start. For HVAC system I routinely work on drives from 1/4HP to 250 HP systems. The basics are the same, enough belt tension so there is no belt slip when running, minimal slip when starting, minimal heat generated, alignment good to excellent depending on drive speed. To make each one perform the best takes more than tension.

    This post has gotten long, so Ill end
    Good Luck