Results 1 to 11 of 11
  1. #1
    Join Date
    Jun 2013
    Posts
    20
    Post Likes

    Crankcase Heaters not required - Goodman

    So I'm reading this Goodman install manual for split systems: https://www.alpinehomeair.com/relate...structions.pdf

    It says this:

    "SCROLL COMPRESSORS The following should be read prior to installing units with scroll compressors...

    Crankcase Heater

    Scroll equipped units do not have nor do not require a crankcase heater."

    Now I'll have to assume that the double negative "nor do not" is because of an illiterate staff at Goodman, and that they are actually saying that crankcase heaters are not required on Goodman splits with scrolls.

    So, if that's the case, does anyone know why Goodman recommends not installing heaters on scrolls?

    I came across a Goodman HP in MN today (30° F this morning) with no heater, and according to this manual that's the way it should be. I'm from FL, working a temp job up here, so I'm learning.
    Last edited by raulsteichen; 11-05-2018 at 12:34 PM. Reason: More information

  2. #2
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    543
    Post Likes
    It will add a extra $5 to there epuipment cost and it will last beyond there warranty without it

    Sent from my SM-G920R4 using Tapatalk

  3. #3
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    543
    Post Likes
    Most equipment will state "crankcase heater must be energized 24 hrs before startup". Then the next unit you look at from the same manufacture wont have any.

    Sent from my SM-G920R4 using Tapatalk

  4. #4
    Join Date
    Dec 2014
    Posts
    2,350
    Post Likes
    Crankcase heaters are often not speced on those smaller units. Unless you have a line length over X number of feet and the charge exceeds X amount. Then they will require crankcase heaters. I'm thinking it's something about the ratio of refrigerant to oil, but I dont know that.


    Sent from my SM-G930V using Tapatalk

  5. #5
    Join Date
    Jun 2013
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by icy78 View Post
    Crankcase heaters are often not speced on those smaller units. Unless you have a line length over X number of feet and the charge exceeds X amount. Then they will require crankcase heaters. I'm thinking it's something about the ratio of refrigerant to oil, but I dont know that.
    This manual is for splits up to 5 tons, and includes tables for linesets up to 75'.

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,833
    Post Likes
    Less of a problem with scrolls. But I would still put one on heat pumps!

  7. #7
    Join Date
    Jan 2010
    Posts
    15,580
    Post Likes
    Scrolls have the capability to push refrigerant droplets through the plates without damage. That's what they claim anyways.
    Does that mean the oil won't be deluted on start up ?
    If yes then how will the bearings react ?

  8. #8
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,121
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Scrolls have the capability to push refrigerant droplets through the plates without damage. That's what they claim anyways.
    Does that mean the oil won't be deluted on start up ?
    If it is then how does the bearings react ?
    Getting a rare flood back to the Scroll and getting those droplets thru the comp is one thing. A Scroll that is subjected to migration, heavy migration and still have the comp survive is a diff story. Depending on the Scroll MN# , some of the "newer" Scrolls have been re-tooled to have "extremely" small passages in between the comp crankcase and the "inlet" to the scroll. Due to the tightness of the avenues of travel for the freon/oil to get from the cc to the scroll,to cause damage, most of that frothing liquid is kept within the confines of the cc. Supposedly!

  9. Likes Spitz liked this post
  10. #9
    Join Date
    Jan 2010
    Posts
    15,580
    Post Likes
    Yes , my question is the oil pickup tube and the change in oil viscosity going up that tube.
    Attached Images Attached Images  

  11. #10
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    543
    Post Likes
    I was taught scrolls are hard to slug. But you can still easily wash out the top bearings with low SH and no CCH.

    Sent from my SM-G920R4 using Tapatalk

  12. #11
    Join Date
    Dec 2014
    Posts
    2,350
    Post Likes
    A crankcase heater will not correct low superheat/ flood back though. The question from the op was why Goodman does not want or does not require crankcase heaters on these compressors. Emerson's application engineering bulletins require crankcase heaters on applications over a certain amount of charge . All low temp Scrolls get crankcase heaters.
    I think Spitz was right partly also in that they're saving a couple of bucks by not putting them on and betting the compressor will outlast the warranty period.
    It's probably not too much of a gamble though I mean they're not stupid and they do have a 10 year warranty on their compressor
    Sent from my SM-G930V using Tapatalk