  1. #14
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    3,451
    Post Likes
    Well the install manual is a little vague, but I found this City Multi bulletin.

    http://meus1.mylinkdrive.com/sfiles/..._Clearance.pdf

    Page 11 shows the S Series side discharge outdoor units. Obviously this different model has difference clearance numbers, but they specifically say no front to back installations.

    MXZ multi head install manual also mentions no front to back.

    Sent from my SM-N910W8 using Tapatalk

  2. #15
    Join Date
    Feb 2014
    Location
    LA CA
    Posts
    66
    Post Likes
    I was at a class for a different brand unit and we were talking about this situation. The trainer suggested to try to use a baffle to throw the air up. I would only try this is as a last resort.

    Sent from my VS988 using Tapatalk

  3. #16
    Join Date
    Jan 2005
    Posts
    41
    Post Likes
    I wouldn't want the headache associated with installing them like that.

  4. #17
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    2,064
    Post Likes
    Dont be these people.....

    Name:  IMG_2222.jpg
Views: 138
Size:  179.0 KB


    Sent from my iPhone using Tapatalk

  5. #18
    Join Date
    Jan 2010
    Posts
    18,033
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Dont be these people.....

    Name:  IMG_2222.jpg
Views: 138
Size:  179.0 KB


    Sent from my iPhone using Tapatalk
    Why would anyone do that ? It's not like they were tight on space !

  6. #19
    Join Date
    Sep 2002
    Posts
    26,903
    Post Likes
    Turn the left one 180 and turn the center one to point away from the wall.

    The only narrower width would be stack them one over the other - all with air intake side facing the wall.

    PHM
    --------------



    t
    Quote Originally Posted by alliedtech12887 View Post
    I’m installing 3 hyper heat condensers on a single pad all in a row. I couldn’t find anything in the Mitsubishi installation docs that call for min clearances between condensers, all I could find was a 20” min tolerance in front of the condenser fan discharge. Does that still apply if you’re putting another condenser in front of the fan discharge? I don’t want to cycle condenser fan discharge air into another condenser and run into issues during the summer. I attached a photo of my ideal layout with 20” between units but not sure if it’s accurate.


    Sent from my iPhone using Tapatalk
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  7. #20
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    2,064
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Why would anyone do that ? It's not like they were tight on space !
    Well..... if I said low bid would you need to ask anymore questions?



    Sent from my iPhone using Tapatalk

  8. #21
    Join Date
    Jan 2010
    Posts
    18,033
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Well..... if I said low bid would you need to ask anymore questions?



    Sent from my iPhone using Tapatalk
    So low bid equates to no brains ?

  9. #22
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    40,509
    Post Likes
    I gotta get a pix of a new motel near me. 3 minis just like jbh posted then the last one blows right in the side of a builder Carrier cube condenser! I bet it runs some high heads next summer!

  10. #23
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    2,064
    Post Likes

    Installing multiple Mini Split Condensers on a single pad clearances.

    Quote Originally Posted by VTP99 View Post
    So low bid equates to no brains ?
    Its pretty much the mo of this company as a whole. Everyone in town knows it. Even the GCs that hire them job after job. No one will touch their prices.
    Its been said they will install a new construction house all equipment and duct for 3500. I cant confirm that though it would not surprise me.
    Most HVAC contractors love this company because they do a great job keeping everyone busy.

    On this same job the guy pulled deep vacuums by the sound of the pump. Brazed lines with no nitro. Ran condensate Drain lines 125 using the mini pumps. Ran lines above manu max recommended length. I can go on.

    Someone told me the install guys are paid by the job, so everything is a race. Again cant confirm.

    I posted maybe 2 years ago on wos with some really winners of this same building.


    Sent from my iPhone using Tapatalk