    Hoshizaki 450MAH shutting down during freeze cycle with no alarms.

    I have a 2001 Hoshizaki 450 MAH that has started shutting down in the middle of the freeze cycle. Then after a minute or 2 it starts back up, goes thru its fill, then harvest and into its freeze cycle. About a minute after the fan comes on, the unit just shuts down. No lights on the board, no trouble beeps, nothing. Can anyone help?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    17,078
    Post Likes
    At 17 how long do you expect it too last?

    Any beeps when restarting?

  3. #3
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    1,643
    Post Likes
    If it completely drops out I would clean the condenser. Maybe high pressure switch is opening.

  4. Likes bigboi0523 liked this post
  5. #4
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    953
    Post Likes
    Bin switch.

    Are you a tech or equipment owner?

  6. #5
    Join Date
    Nov 2018
    Location
    Chesterton, In.
    Posts
    3
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    At 17 how long do you expect it too last?

    Any beeps when restarting?
    Only beep I get, is the fast beep for power check.

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    17,078
    Post Likes
    then its loosing power somewhere.

    I suggest you call your service provider but at that age?

  8. #7
    Join Date
    Nov 2018
    Location
    Chesterton, In.
    Posts
    3
    Post Likes
    Thread Starter
    Thanks mofotech and everyone else who chimed in to help. This morning I cleaned the hell out of the condenser coils. After making a mess of my porter's floors, i plugged her back in and be hold she is cycling through with no problem and producing ice. I will have my apprentice keep an eye on her over the weekend and start on the other (3) 17 year olds. Thanks again.

  9. #8
    Join Date
    Apr 2004
    Location
    Waterloo N.Y.
    Posts
    2,202
    Post Likes
    Prolly had 17 yrs of dirt!
    There's TREACHERY AFOOT!!!

  10. #9
    Join Date
    Jan 2010
    Posts
    14,195
    Post Likes
    I never did like that reverse air direction on the Hoshizaki
    Actually I still service a old R22 Scotsman with the same thing.

  11. #10
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,404
    Post Likes
    Quote Originally Posted by HooChi View Post
    Thanks mofotech and everyone else who chimed in to help. This morning I cleaned the hell out of the condenser coils. After making a mess of my porter's floors, i plugged her back in and be hold she is cycling through with no problem and producing ice. I will have my apprentice keep an eye on her over the weekend and start on the other (3) 17 year olds. Thanks again.
    Poor feller's got it rough. Cleaning it messed up their floors...and he still has 51 years (3x17) worth of more messes to make.

    My sympathies...
    ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° ° °

    "You never know what others don't know." -

    If I can't laugh at myself...then I'll laugh at YOU! -

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.