    There is a need to run copper wires for electric heater. The heater will be three phase, 208 V 37 A.
    Can #8 gauge be used or the distance of 150 feet to the breaker panel would require #6 gauge?

  2. #2
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    5,419
    Post Likes
    My immediate response is to go #6, but, ...... That is without doing any Calculations sigma.
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  3. #3
    Join Date
    Jan 2019
    Location
    huntington beach calif
    Posts
    7
    Post Likes

    wire size

    Quote Originally Posted by sigma View Post
    There is a need to run copper wires for electric heater. The heater will be three phase, 208 V 37 A.
    Can #8 gauge be used or the distance of 150 feet to the breaker panel would require #6 gauge?
    1.73 x 208 = 359.84

    359 x 37 = 13,283 watts

    # 6 for sure