Results 1 to 7 of 7
  1. #1
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    230
    Post Likes

    Oversized boiler replacement

    Replaced a oversized process boiler with a high efficient NTI. Isolated the boiler with a plate heat exchanger. Since install over a year ago more piping has been added to the process side. Been working great

    Sent from my SM-G920R4 using Tapatalk

  2. Likes Metalman0880 liked this post
  3. #2
    Join Date
    May 2006
    Posts
    3,248
    Post Likes
    why all the water stains running down the old boiler exhaust piping did it leak? the new set up looks grate

  4. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    2,751
    Post Likes
    Depending on the water temperature that you are running you might be OK, but I always cringe when I see PVC piping used for a boiler's flue pipe. The maximum temperature that PVC is rated for is 140F. Most boilers run hotter than that. In your install manual it probably says something about either using CPVC for the entire flue run, or at the very least starting your vent piping with a short chunk of CPVC before transitioning to PVC and then setting the boiler to run at a lower maximum temperature. If I'm not mistaken, these boilers even come with a short piece of CPVC for you to use.
    If at First You Don't Succeed, Skydiving Is Not for You.

  5. #4
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    230
    Post Likes
    Thread Starter
    There is a short piece of grey cpvc on the exhaust on the left. Think it is only about 6 inches or so cant see it real well.

    Sent from my SM-G920R4 using Tapatalk

  6. #5
    Join Date
    May 2006
    Posts
    3,248
    Post Likes
    why was the old boiler all stained up with what looks like condensation running down one side

  7. #6
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    230
    Post Likes
    Thread Starter
    Roof leak

    Sent from my SM-G920R4 using Tapatalk

  8. #7
    Join Date
    May 2006
    Posts
    3,248
    Post Likes
    dam that was one heck of a roof leak