    I have a 4-pipe heating/cooling system in a church. One of the fan/coil units is experiencing extremely low flow rate through the hot water coil. All the other fan/coil units work OK. I have blown high-pressure air through the problem coil and feel confident that the coil is not blocked. What are problems that could inhibit water flow through a how water coil that is not blocked? Any ideas would be apopreciated.
    Feb 2011
    Chicagoland
    Appears to be blockage before, or after, the coil then. Find a good thermal camera, or at least a thermocouple thermometer, and take some measures.
    Trying blowing Regulated Nitrogen or CO2 through the coil with the supply and return valves open. Have the Gas enter on the Supply side, or through the Bleeder opening. Blow compressed gas through an empty coil isn't going to do anything.
    Retired, after 43 Years
    Jul 2011
    Charlotte, NC
    Thanks....I can try to get Regulated Nitrogen of CO2 to do this. Also curious about why blowing compressed air through the coil would not do anything??
    Southold, NY
    Quote Originally Posted by Joe Howell View Post
    Is it the coil or the supply return piping?
    Pressure gauges and thermometers are needed!
    Jul 2011
    Charlotte, NC
    It is the coil. There is plenty of flow through the hot water bypass pipe when the thermostat is not calling for heat.
    However, when the thermostat calls for heat, the inlet pipe to the coil becomes hot and the coil becomes warm on the bottom (near the inlet), but becomes progressively cooler toward the top of the coil where the outlet pipe is. It seems that the flow is restricted.
    Dec 2014
    New Mexico
    Pull the coil out and take it outside, pipe it up so you can flush it with a hose both directions it to a bucket to catch what ever is causing the blockage. That way the water treatment company can address the root problem. The flush with a hose provides enough volume to get in to each pass. The unit should have a tag stating max pressure more then likely since one end is going into a bucket you won’t exceed that pressure. Trust me take it out side if you try it in place you don’t have enough rags to clean up the mess when the loose hose comes out of the bucket.
    Sent from my iPad using Tapatalk
    Aug 2009
    Prattville, Alabama
    Since you mention hot water bypass pipe, I take it that the coil has a three-way valve. Is it operating properly? Is it properly installed, with the ports piped up to the proper connections?
    Southold, NY
    How do you know the GPM's? Are there pressure gauges?
    I agree with Nuclrchiller Could be an issue with the control valve!
    Jul 2011
    Charlotte, NC
    Yes, you are right about it having a 3-way valve for hot-water bypass. This valve is installed and operating properly.
    Chicago area
    Can you draw out the piping, all the way back to the source of the supply and return.
    Start there.
    Perhaps a strainer is clogged.
    Its almost impossible to tell if flow is good during bypass.
    Also - is this coil larger or different in some way from the others.
    Is the valve on the supply side or the return side.
    Has it been replaced recently?
    Chicago area
    Is there a balancing valve?
    Chicago area
    Whats the system pressure, and how high up is the coil?