    I'm having issues with a rtac200 closing the alarm relays #1 and #2 for a "low chilled water temp: unit off" in the colder nights. The temp will typically be around 36 and 38* ENT/leaving when I arrive in the am and will show the alarm which is auto reset. I have changed the alarm options to latching alarms only which has taken care of the problem but there is no way to have a circuit specific latching alarm relay. So I have no way on the front end to know if either circuit is in alarm or both. I do have glycol in the system and pump control set above my freeze point for protection. The configuration in the chiller for evap is "with freeze protection". Also i will get alarm for evap water flow overdue as the chiller wants to control the pump but the bms is and sometimes a low evap temp unit off.
    May 2012
    California
    What are you trying to do have it not generate the low water temp alarm?
    Sent from my SM-G930V using Tapatalk
    Nov 2011
    GA
    What is your question?
    Sent from my SM-G950U using Tapatalk
    Life's tough, it's even tougher if your stupid
    Jun 2010
    U.A. (upper Alabama)
    Let the chiller control the pump. Problem solved!
  5. Likes BennyD liked this post.
  6. #5
    ottawa canada
    Quote Originally Posted by cperk View Post
    Im sure it says that somewhere in the IOM .........
    OH yeah what was I thinking ......thats the thing that no one ever reads
  7. Likes cperk, BennyD liked this post.
  8. #6
    ohio
    Yes. I don't want it to generate alarms anymore. I looked and couldn't find a setting for this.
  9. #7
    Apr 2017
    The Deep South
    Quote Originally Posted by michael26 View Post
    There is no setting for this.
    It is generating the alarm because you are at risk for damaging the barrel. The IOM requires that the chiller control the evap pump for freeze protection. If the pump were running, I doubt you would be getting this alarm.
  10. Likes cperk liked this post.
  11. #8
    The Hot South
    And right here is the problem. The IOM specifically states that the chiller must control the pumps. There is also a sticker on the front of the chiller that stated this.
  12. #9
    ohio
    Ok. Thanks guys. That's what I was afraid of.
  13. #10
    Feb 2017
    New York
    I don't think there's anything that say you can't control the pump from both. Have 2 RIB relays, one labeled chiller and the other, BMS. That way, if the chiller needs to run the pump, it can. If they want to cycle it through the BMS, it can. If the BMS crashes, you can still run the chiller in local and it'll control the pump.
    Just a thought.
    -----Stop, step back, relax and have another go at it.-----
  14. #11
    The Hot South
    Quote Originally Posted by BennyD View Post
    Just a thought.
    That is allowed and done all the time.
  15. Likes BennyD liked this post.
  16. #12
    ohio
    Good idea. Thank you
  17. #13
    Aug 2009
    Prattville, Alabama
    Don't forget to include automatic isolation valves in the pump control, if there are any.