    I need a bit of help. So I'm on a job site with another technician and he's working on a mini split Mitsubishi unit. He told me that he thinks it's a dirty coil. So I check the split and it's not a 20 degree split. He then sprays water into the outdoor coil and indoor coil with a spray bottle and the supply temp drops. He checked the split right after with the coils still wet. Was that the correct way to do that? Wouldn't the water still on the coil cause the supply to drop? Just out of curiosity.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Unless the coil is MADE to be wet, then have to wait until it is dry before you can accurately determine most problems.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    If it's a dirty coil, you clean it and then you let it dry.....and then you can evaluate performance from there, based upon the Mitsubishi test standards.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #4
    Join Date
    Sep 2018
    Location
    Cleveland ohio
    Posts
    27
    Post Likes
    I would let it dry , Mitsubishi tec support is pretty good, it never hurts to call with questions, God knows i do.

  5. #5
    Join Date
    Mar 2016
    Location
    NY
    Posts
    415
    Post Likes
    Was it maintenance or service call? What exactly was the split you read? Were the filters and blower wheel clean? And the above posters are right, let it dry even if it’s the evap (yeah yeah I know it’s wet already but it’s not Niagara Falls) and recheck.

  6. #6
    Join Date
    Jun 2018
    Location
    Tualatin, OR
    Posts
    47
    Post Likes
    Thread Starter

    Confused

    Quote Originally Posted by Bombboy90 View Post
    Was it maintenance or service call? What exactly was the split you read? Were the filters and blower wheel clean? And the above posters are right, let it dry even if it’s the evap (yeah yeah I know it’s wet already but it’s not Niagara Falls) and recheck.
    This was a service call. The filters were clean and the blower wheel was slightly dirty but nothing that I believe would cause a problem. I normally allow the coils to dry. But I just started at this company and they wanted me to ride around with another technician for a while and kinda see how he goes about doing his job. I did nothing on the call but check the temperature split. I can't remember the exact reading but I recall getting like 66 f out of the supply. This is a server room by the way. I guess what I wanted to know or understand is that if I left water on the coils and checked the split wouldn't that cause the supply temp to drop and make it seem as if it's cooling better?. I've never checked a unit with wet coils. He saw it drop for a couple of seconds and called it good and then we left.

  7. #7
    Join Date
    Apr 2012
    Posts
    25,995
    Post Likes
    If the supply is cooler after wetting the evaporator.. then it's working as an evaporative cooler.
    Mini splits generally have a larger split due to lower cfm of air per ton...so 66 supply is bad anyway. Unless it was pretty warm in the server room.
    As a side note a wet coil reduces airflow a little making a slightly larger split
    Anyway it sounds like the coil wasn't getting below the dew point of the air...when he wet the coil (evaporator)it was using evaporative cooling which increased the split

    When he wet the outside coil the unit gained capacity as it was also evaporating water which made the dry bulb temperature simulate the wet bulb temperature of the outside air.
    ...

  8. Likes thatguy liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •