    Ruud Furnace Ignition Issue

    working on a ruud silhouette ii model number UGPH-07EAMGR furnace with an ignition issue. unit cycles properly, blower, pressure switch closes, gas valve opens but no spark for the ignitor. checked post on board for the ignitor with a wire to ground and got a single spark out of it during the ignition cycle. assumed it was the ignitor and replaced it, no luck. could the lack of a pulsating spark from the board be the result of a bad ground? also, the unit had had a freeze up issue due to dirty filter, created a lot of condensation which may have dripped down into the unit. Thoughts?

  2. #2
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    We cannot give technical advice in the AOP forum.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  3. #3
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Is it a spark or hsi ignition?
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  4. #4
    Join Date
    Oct 2018
    Posts
    3
    Post Likes
    Thread Starter
    It is a spark ignition.

  5. #5
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    833
    Post Likes
    Quote Originally Posted by jmiller0394 View Post
    It is a spark ignition.
    Stay away from the ICM aftermarket board. Go OEM.

  6. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    If you had a wire to case ground and held other end to the spark terminal, and no sparky, then the board is the issue.

    The spark will overcome a lousy ground and some bad connections. The spark needs to jump an air gap and will.




    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Oct 2018
    Posts
    3
    Post Likes
    Thread Starter
    Thanks for the reply.

    There is a single spark only. It doesn’t repeat or continue to spark say for 5 seconds or so. It doesn’t light with the single spark. I can light it during that cycle with a lighter and everything fires up, so I know the other interlocks are working. Sounds like the board is bad or going bad, correct?

    Yes OEM for sure.

  8. #8
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    What have you learned about it by testing with a meter?
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    If it sparked once , it can surely spark 100 times , so im going with board bad

  10. #10
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    You have not given us anything in the way of a measurement. A real tech would give us some.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •