    Quote Originally Posted by Olivero View Post
    Okay, so 1* would be vapor.

    Theoretically.
    Yes. Theoretically 1* of SH is enough.

    I've taken a couple Copeland classes thru RSES and I've always heard 20-30* at the compressor is ideal. I can also tell you that I've seen extended runs that were poorly insulated with 40-60*SH and the compressors ran just fine.

    Ideal evap SH should be 4-8 on low temp and 8-12 on med temp.

    All the txv adjusting in the world won't bring down compressor SH if the suction line is poorly insulated
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  2. #22
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    2,892
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    Copeland says that they are concerned about the comp SH,not the evap SH. So, having a higher evap SH is the less of two evils. Protect that comp.
    as usual you are correct ... but you can do both, protect the compressor and also ensure system performance .... IE, heat exchanger, suction line accumulator .... ICE is the expert here

    this link clearly states it is preferred NOT to adjust the TXV to obtain the 20 degree minimum

    https://www.achrnews.com/articles/96...ding-superheat

    HOWEVER, as has been pointed out previously some manufacturers DO specify to adjust the TXV to obtain the 20 degree minimum, my point is you do not starve the evaporator or impair system performance to achieve this ... just look over the system and evaluate how it is performing, maybe the system will operate fine running with a higher evaporator outlet superheat, maybe the evaporator outlet superheat needs to be lowered and the 20 degree minimum total superheat needs to be addressed by installing a heat exchanger or an accumulator ? we are all supposed to be competent HVACR people we should be able to evaluate a system and figure that out .....

    for example, the recent post about the True ice cream dipping freezer .... it was designed for a capillary tube, my guess it was probably running with a 10 - 15 degree superheat at the compressor, that is fine, a capillary tube is not going to spiral out of control and slug or flood the compressor under low load conditions because you can adjust the thermostat and charge to prevent that from happening, but then it was converted to a TXV, so what do you do, starve the evaporator coil that is supposed to be almost flooded to obtain the 20 degrees or install a heat exchanger ?

    what about the thread about the freezing evaporator coil, OP adjusted the charge / TXV to obtain 40 degrees at the compressor and was left with a 2.7 degree evaporator temperature, medium temperature ?

    what about the 70 year old Pepsi cooler that ran a high superheat with a cap tube and the compressor got warm and seized ?

    last I knew nobody ever said there was an easy or simple way to do this type of work if you want it done right
    Last edited by hvacskills; 10-15-2018 at 08:19 AM.

  3. #23
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    2,892
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    Copeland says that they are concerned about the comp SH,not the evap SH. So, having a higher evap SH is the less of two evils. Protect that comp.
    you, and most of the other guys on this website have far more experience and are far more knowledgeable in refrigeration than myself, so I am not or am not claiming to be an expert ( except maybe for medium temperature cap tube units ), but I think I understand this part

  4. #24
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,720
    Post Likes
    Thread Starter
    Interesting point you bring up.

    If I were to choose myself, I would rather ensure the comp is getting the right temp gas back to it so it remains cool and doesen't get slugged over the effeciency of the evap.

    If it were a different unit that gets a much higher load and has a much harder time keeping up, I would and I have spent much longer on getting the SH dialed in but this one seems to be happy. It's an R22 medium temp system so with a SH at the evap of 10-15* and the comp at 20-25* I'd say it's pretty good.

    Line's are all well insulated, luckily 80% of the run is easily visible and accessible so I can see it.

  5. #25
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    By Copeland saying they want no less than 20*F SH at the compressor, they are simply building in a huge safety margin. Nothing more, and nothing less.

    The reality is that you will see a wide variation between applications and temp ranges. For example, the older Manitowoc ice machines were dialed in at 1-2*F evap SH right before harvest. Don't know if they still do that.



    Quote Originally Posted by Olivero View Post
    Interesting point you bring up.

    If I were to choose myself, I would rather ensure the comp is getting the right temp gas back to it so it remains cool and doesen't get slugged over the effeciency of the evap.

    If it were a different unit that gets a much higher load and has a much harder time keeping up, I would and I have spent much longer on getting the SH dialed in but this one seems to be happy. It's an R22 medium temp system so with a SH at the evap of 10-15* and the comp at 20-25* I'd say it's pretty good.

    Line's are all well insulated, luckily 80% of the run is easily visible and accessible so I can see it.
    I do a triple evac with nitro to remove non condensables.

  6. #26
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,720
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    By Copeland saying they want no less than 20*F SH at the compressor, they are simply building in a huge safety margin. Nothing more, and nothing less.

    The reality is that you will see a wide variation between applications and temp ranges. For example, the older Manitowoc ice machines were dialed in at 1-2*F evap SH right before harvest. Don't know if they still do that.
    Right, which makes sense. Kind of a way of idiot proofing it by giving you such a large margin of operation.

    I wasn't aware that the droplets were present or even presenting a problem, so I'm glad I now know that.

    Your signature made me laugh, a co worker and I actually did solder a relay onto a scotsman control board by soldering wires to the board so they were sticking out and then soldered the relay onto those wires, worked for months.

  7. #27
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    2,892
    Post Likes
    Quote Originally Posted by BBeerme View Post
    By Copeland saying they want no less than 20*F SH at the compressor, they are simply building in a huge safety margin. Nothing more, and nothing less.

    The reality is that you will see a wide variation between applications and temp ranges. For example, the older Manitowoc ice machines were dialed in at 1-2*F evap SH right before harvest. Don't know if they still do that.
    that is why it is nice to understand ' why ', allows you to adapt to different situations

    walk in cooler I service, older circular evaporator coil with a built in heat exchanger, liquid line running about 4 feet inside the suction line ....

    in the summer with a heavy load the unit runs fine with steady evaporator outlet superheat of 10 - 12 degrees

    last winter with a light load the walk in cooler would reach temperature in around 4 minutes, not long enough for the TXV to stabilize, TXV was hunting all over the place and the evaporator outlet superheat was running low at times, figured this must be the low load they are talking about and how the TXV cant maintain superheat, because of the heat exchanger I still had superheat at my compressor so I just bumped up my box temperature a few degrees as an extra cushion so the load wasnt ' as low ', figured who needs ice cold beer in the winter time anyhow

    understanding ' why ' allowed me to adapt to that situation

  8. #28
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,720
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacskills View Post
    that is why it is nice to understand ' why ', allows you to adapt to different situations

    walk in cooler I service, older circular evaporator coil with a built in heat exchanger, liquid line running about 4 feet inside the suction line ....

    in the summer with a heavy load the unit runs fine with steady evaporator outlet superheat of 10 - 12 degrees

    last winter with a light load the walk in cooler would reach temperature in around 4 minutes, not long enough for the TXV to stabilize, TXV was hunting all over the place and the evaporator outlet superheat was running low at times, figured this must be the low load they are talking about and how the TXV cant maintain superheat, because of the heat exchanger I still had superheat at my compressor so I just bumped up my box temperature a few degrees as an extra cushion so the load wasnt ' as low ', figured who needs ice cold beer in the winter time anyhow

    understanding ' why ' allowed me to adapt to that situation
    Exactly, that's why I wanted to get a better understanding of it.

  9. #29
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Quote Originally Posted by Olivero View Post
    Right, which makes sense. Kind of a way of idiot proofing it by giving you such a large margin of operation.

    I wasn't aware that the droplets were present or even presenting a problem, so I'm glad I now know that.

    Your signature made me laugh, a co worker and I actually did solder a relay onto a scotsman control board by soldering wires to the board so they were sticking out and then soldered the relay onto those wires, worked for months.
    I do a triple evac with nitro to remove non condensables.

  10. #30
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by BBeerme View Post
    By Copeland saying they want no less than 20*F SH at the compressor, they are simply building in a huge safety margin. Nothing more, and nothing less.

    The reality is that you will see a wide variation between applications and temp ranges. For example, the older Manitowoc ice machines were dialed in at 1-2*F evap SH right before harvest. Don't know if they still do that.
    It is my understanding that ice machine compressors have beefier internal parts than low or med temp pumps
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  11. #31
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    If memory serves, ice machine compressors are medium temp.

    For what it is worth, compressors can handle those minute droplets of refrigerant entrained in the oil. Just think about a hot gas defrost, when the evap is actually being used as a condenser. As long as the oil in the compressor is plenty warm, then you're good to go.



    Quote Originally Posted by 2sac View Post
    It is my understanding that ice machine compressors have beefier internal parts than low or med temp pumps
    I do a triple evac with nitro to remove non condensables.

  12. #32
    Join Date
    Nov 2018
    Location
    Cape Coral Fl
    Posts
    34
    Post Likes
    Where and when has Dick Wirz stated at 5*SH liquid refrigerant is present? I personally own a few tomes of his, and do not remember anything of the sort?

  13. #33
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Ive seen oil sight glasses churning and boiling at 8 or better SH.


    Sent from my iPhone using Tapatalk

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •