    Delta GCL+ Cycle Timer

    Good afternoon,
    I am working on trying to program a cycle timer with ORCA... Trying to cycle pumps continuosly every 10 minutes during cold weather... 10 mins on and 10 mins off...
    I am not the Delta genius... I think I am close and can play around some more tomorrow... but wondering if any Delta pros can weigh in on this...

    For instance...
    IF OAT<45 THEN
    (PUMP = ON) AND (LOWTEMP = ON)
    END IF
    IF (PUMP = ON) ONFOR 10M
    (PUMP = OFF)
    END IF
    IF (LOWTEMP = ON) AND ((PUMP = OFF) OFFOR 10M) THEN
    (PUMP = ON)
    END IF
    IF (LOWTEMP = OFF)
    PUMP = OFF

  2. #2
    Join Date
    Dec 2014
    Location
    Vancouver, BC
    Posts
    34
    Post Likes
    The tricky thing with the OnFor and OffFor is that they should really be called "True For" and "False For"
    So if you write the following:
    If (BV1 = Off) OffFor 5M then
    BV2 = On
    EndIf
    That is a double negative, it will execute when BV1 has been ON for 5 minutes.

    Also, when commanding multiple things within one If statement, just write to them on the next line. Using the AND operator asks a question it doesn't write to the point.

    Here's what you are looking to do:

    //ENABLE/DISABLE LOW TEMPERATURE MODE
    If OAT < 45 Then
    LOWTEMP = On
    End If
    If OAT > 50 Then
    LOWTEMP = Off
    End If

    //CYCLE PUMP ON 10 MIN INTERVALS WHEN LOW TEMP MODE IS ACTIVE
    If (LOWTEMP = On) And (PUMP OffFor 10M) Then
    PUMP = On
    End If
    If PUMP OnFor 10M Then
    PUMP = Off
    End If