    I've created a page so that the tech's can review a group of rooms current conditions. They can then tab over to the next page and shut the out of range high/low alarms algorithm off while they are working on it. Problem is they don't always re-inable the alarms. Is there a way to put a time limited reset on it?

  2. #2
    Join Date
    Oct 2018
    Posts
    2
    Post Likes
    Thread Starter
    The thought is that after a given time, say 6 hours, they should have it fixed and the alarms will automatically be re-inabled.

  3. #3
    Join Date
    Dec 2011
    Location
    King of Prussia, PA
    Posts
    9
    Post Likes
    I'm assuming you're using a button on your graphic to a point that disables alarming. Instead of selecting the point as your ORD, expand the point and select the "Override" property. Add a note instructing the tech to select an override duration needed for repairs to be completed

    Sent from my SM-G930V using Tapatalk

  4. #4
    Join Date
    Mar 2016
    Location
    Queensland
    Posts
    100
    Post Likes
    I agree that using the override facility, with only a timed override available, is the way to go. Unfortunately I still can't recall how to limit the override options for the user.
    But if we've understood how you're doing it, you could add a delay to off into your logic so that it switches your Disable command off after your set time.

  5. #5
    Join Date
    Jan 2003
    Location
    USA
    Posts
    3,699
    Post Likes
    Assuming its a boolean writable point, you can add a max override facet to limit how long. If you linked right to the alarm extension inhibit, don't think you have any way to put a limit on it.

    https://hvac-talk.com/vbb/showthread...ide-time-in-ax
    Propagating the formula. http://www.noagendashow.com/

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.