    Having an issue with a high efficiency Westinghouse furnace tripping the manual reset limit mounted to the top of the sealed burner box.
    Aug 2015
    Buffalo,NY
    That’s interesting. I can think of half a dozen reasons off the top of my head. Unfortunately you give no one anything to go on. Sounds like you should get that problem fixed though. Could wind up being serious.
    So what have you checked so far?
    Cincinnati, Ohio
    That usually trips because there is a blockage in the heat exchanger or vent system. One would think the air proving switch would trip but that is rarely the case unless the flue is 100% plugged.
    captain CO
    Aug 2018
    It’s a very short concentric flue. I took it apart and couldn’t find any blockage. In my experience there would be some sort of discoloring of the inside of the burner box. It looks great. The only other thing I can think of is the inducer. I had a unit years ago doing the same thing and changing the inducer fixed it.
    Jul 2018
    Wisconsin
    Stick a analyser in it
    Sep 2015
    Ontari-ari-ari-o
    It's rare but the limit could be faulty I had one that would trip almost as soon as the metal got warm to the touch. How long between limit trips? Also who is making Westinghouse is it a rebadged York or Goodman?
    Aug 2018
    I’m gonna replace the limit and see what happens since I can’t find anything else . It says Westinghouse. I’m not sure if they’re independent or owned by another manufacturer.
    I think its a Nortek made unit.
    Seems to me could be a diffuser on the intake that aims the air intake air away from the burner. It can go in the other way so the air blows on the burner which can cause issues. Might take a look, had this on a Tappan a few years ago.
    Otherwise, 1-800-4AC-HEAT for tech support.