Page 4 of 4 FirstFirst 1234
Results 40 to 46 of 46
  1. #40
    Saint Augustine, Florida, United States
    Interesting
  2. #41
    Shunt is when a winding shorts to itself or another winding, but at a point that has enough resistance to prevent the motor from tripping the breaker.
    Similar to, but not the same as 2 of the speed taps being energized at the same time.
  3. #42
    Jun 2018
    Colorado Springs
    What would be the symptoms of that? Is the only way to see it with a megohmeter? Or would I be able to see it ohming windings
  4. #43
    Quote Originally Posted by digidoggie18 View Post
    Megger won't show it. Ohming might, if you have an identical motor to reference it to.
  5. #44
    Jun 2018
    Colorado Springs
    What would be an ideal way to test for it then VS guessing?
  6. #45
    Motor spinning at a slower speed then it should, and over heating. But turns freely when de energized.
  7. #46
    Jun 2018
    Colorado Springs
    Exactly what I thought, thanks for that!