Thread: Unit Icing up

  1. #1
    Join Date
    Oct 2018
    Posts
    13
    Post Likes

    Unit Icing up

    I have a Goodman CPLE36-1 condenser(heat pump) paired with a AR36-1 air handler with coil. Unit started icing up. Another tech replaced the compressor, but the unit is running the same.

    R22 System
    Suction Pressure 65
    Discharge Pressure 150
    Suction Line Temp 68F
    Discharge Line Temp 90F

    I also found in cooling that the discharge line into the reversing valve is 112f and the outlet is 82F. The suction in is 63F and out is 63F. To me it seems to obviously to be a restriction in the reversing valve but I can not find any source confirming my suspicion.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    What’s the CFM’s?
    What’s your SH & SC?

    How does a reversing valve get restricted?

  3. #3
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,308
    Post Likes
    Believe Goodman put driers even in that model number years, if so did the Tech at least replace or removed it from the outdoor unit.

    What was the justification for replacing a compressor if indoor coil was icing?

    Indoor coil clean.

    What where your pressure reading and temperature difference when in heat mode?

    What was the OD temperature when you got the 150 PSI head pressure in cool mode, as that's certainly low.

    Metering device at ID coil what piston/TXV

    Odd that the temperature drop across the discharge side across RV has a big differential but suction is OK
    Last edited by Bazooka Joe; 10-04-2018 at 04:50 PM.

  4. #4
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    Haven't checked cfm, rookie move, but the indoor coil and fan blades are clean. SH 30F and SC 7F.

  5. #5
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    I am confused!

    How does one condemn a compressor on a unit that is having freezing issues? My cheat sheet says freeze ups are caused be low air flow or low refrigerant flow, without going into much detail. Low refrigerant flow from a bad compressor would not typically freeze a coil.

  6. #6
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    Driers are new

    Compressor replaced because the tech believed in had weak/bad valves

    Didnt check in heat, another rookie mistake

    OD temp 75F

    piston metering device. Previous tech checked both orifices ,one at evaporator and another at condenser, for restriction.

    The temp drop across RV on the discharge but no change on the suction is why I think it has a restiction.

  7. #7
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    Honestly dont know. I'll have to check the cfms and take measurements in heat mode and see if I can figure out why the tech condemned.

  8. #8
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    Weak valves will raise the suction pressure so it becomes very hard to have a freeze up with bad valves. Your 30 SH/7 SC is the clue you need to check into.

  9. #9
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes

    Unit Icing up

    Do you have a temperature drop? What are the dimensions of the supply and return trunks? Piston size?

    If you’re going back, take static pressure too.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by BNME8EZ View Post
    I am confused!

    How does one condemn a compressor on a unit that is having freezing issues? My cheat sheet says freeze ups are caused be low air flow or low refrigerant flow, without going into much detail. Low refrigerant flow from a bad compressor would not typically freeze a coil.
    You must not have the updated cheat sheet.

    Sent from my Moto Z (2) using Tapatalk

  11. #11
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,308
    Post Likes
    I have the CPLJ model, with a discharge muffler and looked up the CPLE model and it shows a discharge muffler also. When you checked the RV temperature difference where you approx. 4"-6" away from the RV body on both sides on the discharge side and downstream of the muffler ( if muffler is still there ) and 4"-6" away from the valve body on the suction side? I have issues with the wide temperature differential on the discharge side but the suction is OK. If at worst case it's not shifting 100% then your suction should have a bigger differential.

    If that temperature of that discharge line downstream of the RV is only 82 degrees ( cooling mode ) and if it's 82 in heating ( reason why you need to check heat mode ) then the Heat side will not work.

    You can also wire the RV to manually shift yourself from cool/heat and vise versa in front of you. You have the low voltage right there.

    If you get back to the job site check in heat mode taking accurate temperature readings with accurate probe secured to the RV lines 4"-6" away from body. Run unit for at least 5+ minutes before taking reading. What are you using to take those readings?

    Put in heat mode then touch vapor line by OD unit. At 75 degree OD temperature you shouldn't be able to touch line.

    Lastly the 150 PSI head pressure is quite low at 75 degree OD temperature. May want to partially cover OD coil to see if pressures rise.

    How did he charge it? Weight method, superheat?
    Last edited by Bazooka Joe; 10-04-2018 at 07:21 PM.

  12. #12
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    Quote Originally Posted by shellkamp View Post
    You must not have the updated cheat sheet.

    Sent from my Moto Z (2) using Tapatalk
    Send me the new one and I will break out the decoder ring.

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    What was the indoor wetbulb. How long is the line set.

    Recover charge and see how much it has in it, and if it adds up to factory charge plus what the line set requires.

  14. #14
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    14,412
    Post Likes
    My guess is the guy who changed the compressor because the system was freezing up, doesn't know how to charge the system correctly either.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    When you appreciate what you have, you have a lot more.

  15. Likes heatingman liked this post.
  16. #15
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by garyed View Post
    My guess is the guy who changed the compressor because the system was freezing up, doesn't know how to charge the system correctly either.
    Or change s compressor!

  17. Likes lions_lair liked this post.
  18. #16
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    UPDATE

    Static Pressure is .2inwc but duct work was clearly added on in the past and incorrectly
    Actual charge is 6.5 lbs Factory Charge is 6.4
    Line set is 30ft
    Outdoor Ambient 85F

    IN COOLING
    Indoor delta T 20F
    Suction Pressure 65psi=38F
    Suction Line Temp 62F
    Superheat 24F
    Discharge Pressure 155psi=85F
    Discharge Line Temp 84F
    Subcool 1F

    IN HEATING
    Indoor delta T 35F
    Suction Pressure n/a due to second service valve being removed for unknown reasons
    Suction Line Temp 73F
    Superheat n/a
    Discharge Pressure 275psi=125F
    Discharge Line Temp n/a
    Subcool n/a

    Reversing Valve In Heat
    Discharge in 178F
    Discharge out 148F
    Suction in 72F
    Suction out 73F

    Muffler before the reversing valve also removed for unknown reasons

  19. #17
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,308
    Post Likes
    The CPLE brochere ( readily available online ) says the data plate charge is correct for 15' of correctly sized lineset and a matching indoor coil. Being a old unit, the weight method IMO was a justified way of charging...with that in mind you have 30' of lineset so taking .60-.62 ounces of liquid line for each feet above the initial 15' gives you 9.15 ounces, so to me your 8 ounces under charged IMO...for starters.

    Still way low on head pressure @85 degree OD temperature, should be at least 210-225 ( cool mode ) give or take...with a 10 SEER UNIT.

    You sure there's a ID piston in that unit?

    Seems like with a new compressor it would be pumping OK but there is no resistance ( metering device ) to slow the flow of refrigerant with that low a head pressure.

  20. #18
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Quote Originally Posted by Snow23 View Post
    UPDATE

    Static Pressure is .2inwc but duct work was clearly added on in the past and incorrectly
    Actual charge is 6.5 lbs Factory Charge is 6.4
    Line set is 30ft
    Outdoor Ambient 85F

    IN COOLING
    Indoor delta T 20F
    Suction Pressure 65psi=38F
    Suction Line Temp 62F
    Superheat 24F
    Discharge Pressure 155psi=85F
    Discharge Line Temp 84F
    Subcool 1F

    IN HEATING
    Indoor delta T 35F
    Suction Pressure n/a due to second service valve being removed for unknown reasons
    Suction Line Temp 73F
    Superheat n/a
    Discharge Pressure 275psi=125F
    Discharge Line Temp n/a
    Subcool n/a

    Reversing Valve In Heat
    Discharge in 178F
    Discharge out 148F
    Suction in 72F
    Suction out 73F

    Muffler before the reversing valve also removed for unknown reasons
    Amperage will help tell you if there is a restriction or not at the RV.

    Since its vapor at the RV - temp drop does not mean alot.

    Seems to me, your just low on gas.

    But you need to plot the Target SH to know for sure.




    Sent from my iPhone using Tapatalk

  21. #19
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    14,412
    Post Likes
    Quote Originally Posted by Snow23 View Post
    UPDATE

    Static Pressure is .2inwc but duct work was clearly added on in the past and incorrectly
    Actual charge is 6.5 lbs Factory Charge is 6.4
    Line set is 30ft
    Outdoor Ambient 85F

    IN COOLING
    Indoor delta T 20F
    Suction Pressure 65psi=38F
    Suction Line Temp 62F
    Superheat 24F
    Discharge Pressure 155psi=85F
    Discharge Line Temp 84F
    Subcool 1F

    IN HEATING
    Indoor delta T 35F
    Suction Pressure n/a due to second service valve being removed for unknown reasons
    Suction Line Temp 73F
    Superheat n/a
    Discharge Pressure 275psi=125F
    Discharge Line Temp n/a
    Subcool n/a

    Reversing Valve In Heat
    Discharge in 178F
    Discharge out 148F
    Suction in 72F
    Suction out 73F

    Muffler before the reversing valve also removed for unknown reasons
    It would be helpful if you gave us at least the indoor dry bulb. The wetbulb would be good too because it would give a better idea of
    what superheat to expect. At this point though the numbers just look like you're a little low on gas. Your delta T looks fine & so does the static pressure. If you had any serious airflow problems you would have a lot higher discharge than 275psi. Even with good airflow I would expect around 350psi at 80* OA in heat mode which is another indication of low charge. There's also the possibility that the instruments where you're getting all the readings are not calibrated properly. Either way I don't see any serious problem at this point & no reason to be changing any more parts.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    When you appreciate what you have, you have a lot more.

  22. #20
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Snow23 View Post
    UPDATE

    Static Pressure is .2inwc but duct work was clearly added on in the past and incorrectly
    Actual charge is 6.5 lbs Factory Charge is 6.4
    Line set is 30ft
    Outdoor Ambient 85F

    IN COOLING
    Indoor delta T 20F
    Suction Pressure 65psi=38F
    Suction Line Temp 62F
    Superheat 24F
    Discharge Pressure 155psi=85F
    Discharge Line Temp 84F
    Subcool 1F

    IN HEATING
    Indoor delta T 35F
    Suction Pressure n/a due to second service valve being removed for unknown reasons
    Suction Line Temp 73F
    Superheat n/a
    Discharge Pressure 275psi=125F
    Discharge Line Temp n/a
    Subcool n/a

    Reversing Valve In Heat
    Discharge in 178F
    Discharge out 148F
    Suction in 72F
    Suction out 73F

    Muffler before the reversing valve also removed for unknown reasons
    It ran long enough in heat with 85°F ambient to get readings?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •