Results 1 to 8 of 8
    Jul 2009
    new york
    Traulsen prep fridge
    That few days temps have been hovering around 56 degrees and I see frost is on the outlet of the TXV. TXV is frozen right after inlet. What would cause this?
    Jan 2010
    Where's this fridge located ? Ambient speaking.
    Jul 2009
    new york
    73 degrees. I vaccumned and pushed nitrogen through system and weighed in 16oz of 134a and still 56 degrees is where it sits with frost on outlet of txv heading to evap
    Jan 2010
    Well you shouldn't have to open the valve but if the power element is losing charge you'll have to do that to by time. What is the superheat ?
    Jul 2009
    new york
    The super heat is 13
    Jan 2010
    It's R134a right ? Suction pressure should be around 15 psig.
    Southold, NY
    Mod # would be nice?
    Grab the bulb and see if the suction goes up.
    Southold, NY
    Better yet
    Pull the drier and valve, install a small receiver, new drier & SG and valve.
    Recharge to clear glass and be done!