Where's this fridge located ? Ambient speaking.
That few days temps have been hovering around 56 degrees and I see frost is on the outlet of the TXV. TXV is frozen right after inlet. What would cause this?
Where's this fridge located ? Ambient speaking.
Well you shouldn't have to open the valve but if the power element is losing charge you'll have to do that to by time. What is the superheat ?
It's R134a right ? Suction pressure should be around 15 psig.
Mod # would be nice?
Grab the bulb and see if the suction goes up.
R I P Icemeister
Supporting our Vet’s
http://www.soldierride.org/
http://www.woundedwarriorproject.org/
Better yet
Pull the drier and valve, install a small receiver, new drier & SG and valve.
Recharge to clear glass and be done!