    Question Carrier iVu Control Programs

    I have a couple of iVu systems on version 6.0 and 6.5. They have several different models of unitary controller:
    • New free-programmable (UC XP)
    • New application specific (RTU Open)
    • Old CCN free-programmable (Comfort Controller)

    And a few types of router:
    • iVu Open Router
    • CIV-CR
    • CCN/Ethernet Bridge


    I've done a lot of programming in WebCTRL, but there are a few differences between it and iVu that I'm trying to figure out.

    1. Will each of those router types accept Control Programs built with SNAP?
    2. Using the Control Program at the router, can I write to remote points to the unitary controllers? Occupancy, setpoint, etc.
    3. Are EquipmentBuilder, SNAP, and ViewBuilder all included in USB-TKIT?
    4. One of the manuals mentioned getting a non-expiring license (rather than the built-in 2 year license) from Carrier... what is that process?

  2. #2
    Join Date
    Apr 2014
    Location
    MN
    Posts
    421
    Post Likes
    1. Yes for the CCN and Open routers, not sure about the Ethernet Bridge (I kind of doubt it).
    2. You should be able to write to remote points in the unitary controllers. If you use a blue Carrier points in the SNAP program and check the box "Enable BACnet Write" it should work. You should also be able to write to points using BACnet Analog and Binary points.
    3. Yes. You can also buy the software only if you already have a USB connection from ALC or Carrier.
    4. I thought the new version 7 did away with the license not 100% sure though. The license update file should be provided for free though, it's nothing you have to buy from Carrier. Other than that if you have a Pro system you can use that license when when you install your tools to prevent the license from expiring.

  3. Likes theGAXman liked this post
  4. #3
    Join Date
    Jul 2012
    Location
    Fort Worth, TX
    Posts
    27
    Post Likes
    Thread Starter
    Great, thanks for the info.

  5. #4
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    70
    Post Likes
    only ccn routers accept programs. open routers do not. open links do. Keep in mind if you change anything, the ccn router can also take place of 4 upc's and can do ccn to open linkage.

    Yes the usb tkit has all installer programs. what you mentioned, app loader, test and balance, and a few others also.
    I have not seen any bulletin for a non expiring license. I doubt they will. it's only issued to carrier controls experts, and unless we recertify yearly it won't be accessed in hvac partners. Just change your computer date, but i didn't tell you that