    CVHF oil pressure problem?

    I have a CVHF that the oil pump discharge pressure sensor reads around 9psi but at the pump im getting 18psi. Do you think it could be a sensor issue or a restriction in the oil line? Also Changed the oil filter and nothing changed. Oil level is good.


    Sent from my SM-G955U using Tapatalk

  2. #2
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,179
    Post Likes
    Does it have an oil cooler?
    -----Stop, step back, relax and have another go at it.-----

  3. #3
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    28
    Post Likes
    Thread Starter
    Yes in the economizer.

    Sent from my SM-G955U using Tapatalk

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,318
    Post Likes
    A quick and easy test to help determine sensor accuracy is to shut down the chiller and the oil pump, then compare the indicated pressure readings of all transducers at the control panel.

  5. #5
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    28
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    A quick and easy test to help determine sensor accuracy is to shut down the chiller and the oil pump, then compare the indicated pressure readings of all transducers at the control panel.
    Well they all read the same, so should i pull the gas and check the oil line?

    Sent from my SM-G955U using Tapatalk

  6. #6
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    680
    Post Likes
    Did you cut the filter open looking for silver?

  7. #7
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,179
    Post Likes
    Those numbers are fine. There will be a pressure drop across the oil cooler and yours seem to be within spec. If you're having oil pressure issues and not losing oil from the sump, you probably have a bad regulator.
    -----Stop, step back, relax and have another go at it.-----

  8. Likes cperk liked this post
  9. #8
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    28
    Post Likes
    Thread Starter
    Quote Originally Posted by BennyD View Post
    Those numbers are fine. There will be a pressure drop across the oil cooler and yours seem to be within spec. If you're having oil pressure issues and not losing oil from the sump, you probably have a bad regulator.
    The sump was empty last week the chiller was idle for months 8+ . They wanted it running so i added 5 gallons of oil and got it running and all the oil came back after a day of running so I drained the 5 gallons back out. It ran fine for a few days.

    Sent from my SM-G955U using Tapatalk

  10. #9
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,179
    Post Likes
    Quote Originally Posted by VanillaGorila80 View Post
    The sump was empty last week the chiller was idle for months 8+ . They wanted it running so i added 5 gallons of oil and got it running and all the oil came back after a day of running so I drained the 5 gallons back out. It ran fine for a few days.

    Sent from my SM-G955U using Tapatalk
    If it's idle, they need to keep the oil heater on. I take it that it's a low sump under the condenser? That's a good sign that it all came back. I'm still pointing to the regulator.
    You're almost there to be eligible for pro membership. Apply and you can get more into the nitty-gritty.
    -----Stop, step back, relax and have another go at it.-----

  11. #10
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,318
    Post Likes
    Check out that oil sump heater. Not just that it's pulling some amps, but that it's pulling the correct amount of amps. That heater is actually a few smaller heaters inside a housing. They're wired in parallel, so a failure of one will still allow the others to operate, but it will not be sufficient. I don't recall what the full amperage is, but I'm sure somebody here will chime in.

  12. #11
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,196
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    Check out that oil sump heater. Not just that it's pulling some amps, but that it's pulling the correct amount of amps. That heater is actually a few smaller heaters inside a housing. They're wired in parallel, so a failure of one will still allow the others to operate, but it will not be sufficient. I don't recall what the full amperage is, but I'm sure somebody here will chime in.
    6 amps give or take a few tenths.


    Sent from my iPhone using Tapatalk

  13. #12
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,179
    Post Likes
    Quote Originally Posted by cperk View Post
    6 amps give or take a few tenths.


    Sent from my iPhone using Tapatalk
    Thanks! I was going to pull a log but totally forgot!
    -----Stop, step back, relax and have another go at it.-----

  14. #13
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,318
    Post Likes
    Quote Originally Posted by cperk View Post
    6 amps give or take a few tenths.


    Sent from my iPhone using Tapatalk
    Thanks, c! I trust y'all a whole lot more than I trust my memory, lol!