    That regulator is not seated correctly so the diaphram is not trapped correctly in the bottom of the recess it sits in . Obviously the regulator has been changed as its not painted green. So whoever changed it put it in crooked .
    Dont pull the gas . Take the bolts out , remove the flange . If its in a vacuum the suction will hold the reg in . You should be able to turn the regulator freely in the hole with some resistance due to the O ring . If you cant turn it its crooked and jammed in the recess . It may suck a bit of air put the diaphram in the bottom will keep most of the air out . Unless whoever installed the reg butchered that too ??
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  2. #28
    Join Date
    Nov 2008
    Posts
    390
    Post Likes
    Just replace the whole block and be done with it.... that can be done on the fly

  3. #29
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,994
    Post Likes
    Quote Originally Posted by triggerhappy View Post
    Just replace the whole block and be done with it.... that can be done on the fly
    With the loosey goosey US refrigerant regulations you can do anything “on the fly”
    Just hold your breath and get er dun
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  4. #30
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,095
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    With the loosey goosey US refrigerant regulations you can do anything “on the fly”
    Just hold your breath and get er dun
    Cannot be larger than 2 square inches if I remember correctly. If it's larger, it's gotta be recovered... at least in NYS.
    I've done regulators on the fly. Usually use a boiler to bring it up close to zero. Never replaced an oil filter block. Wouldn't think there would be a reason to unless the seat is screwed up.
    -----Stop, step back, relax and have another go at it.-----

  5. #31
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    22
    Post Likes
    Thread Starter
    We have a reftec allvac recover machine should be able to recover the charge in about 4hrs.

    Sent from my SM-G955U using Tapatalk

  6. #32
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,095
    Post Likes
    Quote Originally Posted by VanillaGorila80 View Post
    We have a reftec allvac recover machine should be able to recover the charge in about 4hrs.

    Sent from my SM-G955U using Tapatalk
    4 hours? What size is the machine? Charge #?
    -----Stop, step back, relax and have another go at it.-----

  7. #33
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,994
    Post Likes
    Quote Originally Posted by VanillaGorila80 View Post
    We have a reftec allvac recover machine should be able to recover the charge in about 4hrs.

    Sent from my SM-G955U using Tapatalk
    This is what “the sales guy says” ?
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  8. #34
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by BennyD View Post
    4 hours? What size is the machine? Charge #?
    Cvhf570 think it holds 8-900 lbs,

    Sent from my SM-G955U using Tapatalk

  9. #35
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    218
    Post Likes
    You ain't gonna get the charge out in 4 hours. It will take you that long to set it up and push the liquid out. Then at least that long to get the vapor.

    I've done the whole block a couple of times with the machine just slightly below zero. With it off, there are only 4 small holes in the oil sump.

    If you get your pro membership, I could describe the process for you, but not out here in the open.

  10. Likes BennyD liked this post
  11. #36
    Join Date
    Aug 2018
    Location
    Columbus,Ohio
    Posts
    22
    Post Likes
    Thread Starter
    I'll time i should be out there Wednesday. I didnt say anything about setup . I Maybe a little ambitious on the time but should be able to get it in s day i imagine.

    Sent from my SM-G955U using Tapatalk

  12. #37
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,095
    Post Likes
    I've had a question about recovery units like the one that OP posted a pic of.
    If the chiller has air in it, how do you deal with it? Do you just burp it off the top of the recovery tank? Do you let the purge handle it after charging?
    I only ask because our shop has more or less home made machines that has the ability purge as you recover. We also have a few large reclaimers that will distill 700# at a time... takes a while though.
    -----Stop, step back, relax and have another go at it.-----

  13. #38
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,308
    Post Likes
    I hook up our portable purge to the recovery tank when a chiller has a lot of air in it.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

    Technically speaking, they are all heat pumps.

  14. #39
    Join Date
    Nov 2008
    Posts
    390
    Post Likes
    Well if this tells you anything about what think of the climate change fraud that has been perpetrated on the American public...…..I dig holes with my backhoe and fill them in just to burn the diesel fuel....LOL

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.