    Noise at evap coil
    Hi, I was cleaning a residential ac unit last week, and I noticed something weird.
    Whenever the compressor started, there would be a loud whooshing noise at the evap coil, sorta like opening a valve on a tank, except muffled. The noise lasts about 2-3 seconds each time.
    This is a 2.5 ton 410 unit without a txv, about 2 years old.
    Speaking to the homeowner It has done it since new. The unit cools well, and I didn’t hook up the gauges to it.
    Any idea what might be causing this?
    Mar 2014
    Ottawa,ON
    Is this a heat pump or straight ac?
    Aug 2018
    AC
    Mar 2014
    Ottawa,ON
    So did it work fine after u cleaned it? Sure that noise wasnt a big hole in the evap ?
    Aug 2018
    Unit cools good. I only cleaned the condenser coil, the evap was clean.
    Chicago area
    Thats the sound of gas blowing through the metering device. At start up, its mainly gas in the liquid line.
    Jun 2017
    Central FL
    That's normal, gas being pumped through your liquid line as heatingman said. You're never going to start a unit and not heat the refer moving. A constant loud swish might indicate an issue though.
    Dec 2009
    maroon lazyboy
    You can hear it on expansion valves also. Listen for the liquid seal to hit, the “dry” TXVs really whistle.
    Aug 2018
    Quote Originally Posted by knave View Post
    I guess I’ve never heard it that loud before, I was just wondering if it’s normal. I suppose it is. Thanks!
    Jan 2013
    Check the refrigerant pressures, sometimes it’s other things like low refrigerant which can indicate a possible leak,non condensables or not topped off since it’s fairly new.
    Sep 2018
    San Diego
    Quote Originally Posted by heatingman View Post
    ^^^^ THIS ^^^^ Probably a non bleed