    Noise at evap coil

    Hi, I was cleaning a residential ac unit last week, and I noticed something weird.
    Whenever the compressor started, there would be a loud whooshing noise at the evap coil, sorta like opening a valve on a tank, except muffled. The noise lasts about 2-3 seconds each time.
    This is a 2.5 ton 410 unit without a txv, about 2 years old.
    Speaking to the homeowner It has done it since new. The unit cools well, and I didn’t hook up the gauges to it.
    Any idea what might be causing this?

  2. #2
    Join Date
    Mar 2014
    Location
    Ottawa,ON
    Posts
    243
    Post Likes
    Is this a heat pump or straight ac?


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Aug 2018
    Location
    South Dakota
    Posts
    20
    Post Likes
    Thread Starter
    AC


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Mar 2014
    Location
    Ottawa,ON
    Posts
    243
    Post Likes
    So did it work fine after u cleaned it? Sure that noise wasnt a big hole in the evap ?


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Aug 2018
    Location
    South Dakota
    Posts
    20
    Post Likes
    Thread Starter
    Unit cools good. I only cleaned the condenser coil, the evap was clean.


    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thats the sound of gas blowing through the metering device. At start up, its mainly gas in the liquid line.


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Jun 2017
    Location
    Central FL
    Posts
    19
    Post Likes
    That's normal, gas being pumped through your liquid line as heatingman said. You're never going to start a unit and not heat the refer moving. A constant loud swish might indicate an issue though.

  8. #8
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    You can hear it on expansion valves also. Listen for the liquid seal to hit, the “dry” TXVs really whistle.

  9. #9
    Join Date
    Aug 2018
    Location
    South Dakota
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by knave View Post
    You can hear it on expansion valves also. Listen for the liquid seal to hit, the “dry” TXVs really whistle.
    I guess I’ve never heard it that loud before, I was just wondering if it’s normal. I suppose it is. Thanks!


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Jan 2013
    Location
    Virginia
    Posts
    80
    Post Likes
    Check the refrigerant pressures, sometimes it’s other things like low refrigerant which can indicate a possible leak,non condensables or not topped off since it’s fairly new.

  11. #11
    Join Date
    Sep 2018
    Location
    San Diego
    Posts
    45
    Post Likes
    Quote Originally Posted by heatingman View Post
    Thats the sound of gas blowing through the metering device. At start up, its mainly gas in the liquid line.


    Sent from my iPhone using Tapatalk
    ^^^^ THIS ^^^^ Probably a non bleed

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •