    All right new to the forum. I have a problem I can't figure out
    15 ton chiller we had a leak. We evacted the system, fixed the leak.
    vaced the system, and recharged. High pressure is 130# low 25# machine says it takes 22 pounds of r-22. We put over 30 pounds in
    and the sight glass still bubbles. The bubble never went away during charging. air temp is about 90 degrees.
    Ideas????
    Mar 2013
    Billington Heights, NY
    Gross non-condensibles, restriction.
    Mixing oil and fire with a big spoon.
    Quote Originally Posted by HVAC_Marc View Post
    Yep
    "Right" is not the same as "Wise".
    Don't step on my favorite part of the Constitution just to point out your favorite part.
  4. Likes HVAC_Marc liked this post.
  5. #4
    ottawa canada
    Nameplate says 22lbs .......it must work better or cool faster with 30lbs in er ........pound the gas to er , Im gonna get that sight glass clear if it kills me or the compressor liquid locks first
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!
  6. #5
    Apr 2017
    The Deep South
    I will add a X3 or X4 to the above diagnosis.
  7. #6
    Jan 2015
    Somewhere making cold water
    Quote Originally Posted by JCN View Post
    Is that a mathematical approach?
    X3=66lbs X4=88lbs. More gogo gas run better. Lol!
    Sent from my SM-G950U using Tapatalk
  8. Likes HVAC_Marc liked this post.
  9. #7
    Apr 2017
    The Deep South
    Quote Originally Posted by WYLBEK View Post
    Yup. It's more betterer.
  10. Likes HVAC_Marc liked this post.
  11. #8
    Apr 2016
    Maryland
    What micron level does your vacuum pump reach when connected to a micron gauge ?