    All right new to the forum. I have a problem I can't figure out
    15 ton chiller we had a leak. We evacted the system, fixed the leak.
    vaced the system, and recharged. High pressure is 130# low 25# machine says it takes 22 pounds of r-22. We put over 30 pounds in
    and the sight glass still bubbles. The bubble never went away during charging. air temp is about 90 degrees.
    Ideas????

  2. #2
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,628
    Post Likes
    Gross non-condensibles, restriction.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,658
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    Gross non-condensibles, restriction.
    Yep
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

  4. Likes HVAC_Marc liked this post
  5. #4
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    3,202
    Post Likes
    Nameplate says 22lbs .......it must work better or cool faster with 30lbs in er ........pound the gas to er , Im gonna get that sight glass clear if it kills me or the compressor liquid locks first
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. #5
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    332
    Post Likes
    I will add a X3 or X4 to the above diagnosis.

  7. #6
    Join Date
    Jan 2015
    Location
    Somewhere making cold water
    Posts
    228
    Post Likes
    Quote Originally Posted by JCN View Post
    I will add a X3 or X4 to the above diagnosis.
    Is that a mathematical approach?
    X3=66lbs X4=88lbs. More gogo gas run better. Lol!

    Sent from my SM-G950U using Tapatalk

  8. Likes HVAC_Marc liked this post
  9. #7
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    332
    Post Likes
    Quote Originally Posted by WYLBEK View Post
    Is that a mathematical approach?
    X3=66lbs X4=88lbs. More gogo gas run better. Lol!

    Sent from my SM-G950U using Tapatalk
    Yup. It's more betterer.

  10. Likes HVAC_Marc liked this post
  11. #8
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    273
    Post Likes
    What micron level does your vacuum pump reach when connected to a micron gauge ?