    All right new to the forum. I have a problem I can't figure out
    15 ton chiller we had a leak. We evacted the system, fixed the leak.
    vaced the system, and recharged. High pressure is 130# low 25# machine says it takes 22 pounds of r-22. We put over 30 pounds in
    and the sight glass still bubbles. The bubble never went away during charging. air temp is about 90 degrees.
    Ideas????

  2. #2
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    20,923
    Post Likes
    Gross non-condensibles, restriction.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,308
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    Gross non-condensibles, restriction.
    Yep
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

    Technically speaking, they are all heat pumps.

  4. Likes HVAC_Marc liked this post
  5. #4
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,994
    Post Likes
    Nameplate says 22lbs .......it must work better or cool faster with 30lbs in er ........pound the gas to er , Im gonna get that sight glass clear if it kills me or the compressor liquid locks first
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. #5
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    217
    Post Likes
    I will add a X3 or X4 to the above diagnosis.

  7. #6
    Join Date
    Jan 2015
    Location
    Somewhere making cold water
    Posts
    178
    Post Likes
    Quote Originally Posted by JCN View Post
    I will add a X3 or X4 to the above diagnosis.
    Is that a mathematical approach?
    X3=66lbs X4=88lbs. More gogo gas run better. Lol!

    Sent from my SM-G950U using Tapatalk

  8. Likes HVAC_Marc liked this post
  9. #7
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    217
    Post Likes
    Quote Originally Posted by WYLBEK View Post
    Is that a mathematical approach?
    X3=66lbs X4=88lbs. More gogo gas run better. Lol!

    Sent from my SM-G950U using Tapatalk
    Yup. It's more betterer.

  10. Likes HVAC_Marc liked this post
  11. #8
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    255
    Post Likes
    What micron level does your vacuum pump reach when connected to a micron gauge ?