    50 Amps on 8ga SO Rubber wire

    Just hooked up a convection oven , I ran 6 ga over to it off a 60a breaker, and it already has a 6 foot piece of wire coming out from it but its only 8 ga stranded SO

    THis is 3 phase 208 and ive got 49 49 50 pulling each leg

    Since it apparently worked like that, I simply used split bolts to make my connections


    Plus it would be really difficult to run the 6 ga to the contactor they have and make those tight turns . which might be why they used 8


    You think its ok ??

  2. #2
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    20,923
    Post Likes
    No

  3. #3
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    884
    Post Likes
    Nope


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    493
    Post Likes
    Quote Originally Posted by VanMan812 View Post
    Nope
    This ^^^
    With your chrome heart shining in the sun, long may you run.

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,754
    Post Likes
    Thread Starter
    LIARS

    I smell a conspiracy !

    No ! I don't wanna try to stuff that 6 ga in there !

  6. #6
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,377
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    LIARS

    I smell a conspiracy !

    No ! I don't wanna try to stuff that 6 ga in there !


    "You never know what others don't know." -

    If I can't laugh at myself...then I'll laugh at YOU! -

  7. #7
    Join Date
    Apr 2004
    Location
    Waterloo N.Y.
    Posts
    2,156
    Post Likes
    What kind of ovens are you hooking up? I just installed 4 Vulcans and the draw 38A a leg.
    There's TREACHERY AFOOT!!!

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,754
    Post Likes
    Thread Starter
    Hardt Genius 10-11 Combi oven

    Says on electric label draws 51 amps

  9. #9
    Join Date
    Apr 2004
    Location
    Waterloo N.Y.
    Posts
    2,156
    Post Likes
    I'd run # 6 in a seal tight whip
    There's TREACHERY AFOOT!!!

  10. #10
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,754
    Post Likes
    Thread Starter
    Havent went back yet , but the dagone contactor doesn't look like it will even accept 6


    they been using it , so one day soon I will slide by and feel the wires to see if getting warm