    Need assistance with newly installed dehumidifier

    Hi,
    Had new installed ultra-aire 120H installed. House sq is ~3800ft (I missed up and forgot to include unfinished basement when I order this. I was thinking only of the finished footage of 2500sqf). Live in NW Wisconsin (about 40miles from twin cities MN). unit installed to existing return duct; not dedicated duct also connect to outside for venting. House has basement (where HVAC is), 1st floor and 2nd floor with dual zone configured. zone 1 1st floor/basement, zone 2 2nd floor. Currently I have system fan to low for both zones (not the fan on 120H) to keep the zone dampers opened when the 120H does kick in. Tech recommended leaving fan to low even if I didn't have a dehum. I've set the ultra to 44r/h but never reaches that. When a/c isn't running R/H hovers around 48. When A/C get's on it will get down to 40 pretty quick and when a/c turns off it will go back up to about 48. ultra is constantly running. Is the 120H too small? WI climate can get very humid but right now it's not bad so surprise the 120H can't keep up. Not sure if the install isn't right, too small dehum; or I'm expecting too much. I want it @ 44 to help protect my wide plank wood floors from moisture fluctuations.

    Thanks
    Attached Images Attached Images  

  2. #2
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    50%RH will protect floors and eliminate typical moisture problems during times of low/no sensible cooling and high outdoor dew points. I would set the Ultra-Aire 2-3%RH above the level %RH the a/c maintains during long runs. Setting the dehu control below what the a/c provides during high cooling loads assures that the dehu will run alot during high outdoor dew points weather. We have been have very high dew points this summer. Many times the dew point in WI. is as high as FL. Set the dehu to 53%RH and watch the the resulting %RH in the living space.
    I understand you are operating the a/c fan in the "on" low mode 24/7??. This will be needed the way the dehu ducts are connected to the a/c.
    This requires a little more dehumidification but is premium from the stand point of uniform temp/%RH throughout the home. At the 43%RH setting, a larger dehu would probably run all the time.
    Thank you for the opportunity to serve!
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  3. #3
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,269
    Post Likes
    Instead of how you have the dehumidifier piped -supply to return. Pipe it return to return because duct pressure would be close to the same and warmer then trying to dehum the cold supply. Wire dehum with a airflow switch to run when fan runs and you can turn RH control down if dehum short cycles. Is the humidifier damper closed and turned off?

  4. #4
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    That's truly horrible. Who hooked that up? Flex like that is very restrictive. You paid for a good unit and it should be as efficient as possible. I'd suggest hard pipe for all connections.
    Nest is POO!!

  5. #5
    Join Date
    Jul 2006
    Posts
    4
    Post Likes
    Thread Starter
    Thanks for all the replies.
    @Teddy Bear - wood supplier recommend 44-48 for their hickory wide planks (6") would be best. I have dual stage furnace a/c. Evolution shows function off, ac off fan on (when I set to low) when A/C is off. Put it to low to keep the zone dampers opened for the dehum when it kicks on. They didn't wire dehum to furnance to tell it to kick on fan when dehum fan turns on. Before hvac fan was set to auto. When it was first installed the fan was still at auto and I could tell it wasn't working at all for dehumidication when dehumidifier turned on. RH was in high 50's; figure it was because dampers were closed so I turned it on to low to open dampers. Had them come out again to go over the install. Different tech came and was surprised the installer didn't turn on fan to open the dampers. Not sure if they put in back draft damper. would system by more efficient if I have them run a dedicated return duct for dehumidifier?
    @servicefitter - humidifier damper is closed (honeywell; latch set to summer) confirm also humidifier is off in evolution system. My existing ERV is off after installing the dehumidifier since it also does venting. Though I probably turn it back on for winter; not sure about that if erv should be on or leave utlra-aire on for venting (turn off the dehumidifer part)
    @hvac-marc - Ultra-aire provided the HVAC contact which is same HVAC that installed the HVAC system when my house was built. There was no other HVAC installer available in my area for ultra-aire. Unfortunately this installer has never installed dehumidifier; this was their first one. Why I posted here wonder if install was right.

  6. #6
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Is there a damper on the pipe for the bypass humidifier? It should be closed to prevent the air from the dehumidifier from circulating back through it.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  7. #7
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by harlock328 View Post
    Thanks for all the replies.
    @Teddy Bear - wood supplier recommend 44-48 for their hickory wide planks (6") would be best. I have dual stage furnace a/c. Evolution shows function off, ac off fan on (when I set to low) when A/C is off. Put it to low to keep the zone dampers opened for the dehum when it kicks on. They didn't wire dehum to furnance to tell it to kick on fan when dehum fan turns on.

    Before hvac fan was set to auto. When it was first installed the fan was still at auto and I could tell it wasn't working at all for dehumidication when dehumidifier turned on. RH was in high 50's; figure it was because dampers were closed so I turned it on to low to open dampers. Had them come out again to go over the install. Different tech came and was surprised the installer didn't turn on fan to open the dampers. Not sure if they put in back draft damper. would system by more efficient if I have them run a dedicated return duct for dehumidifier?
    Back flow through the dehu is not critical in this case.

    @servicefitter - humidifier damper is closed (honeywell; latch set to summer) confirm also humidifier is off in evolution system. My existing ERV is off after installing the dehumidifier since it also does venting. Though I probably turn it back on for winter; not sure about that if erv should be on or leave utlra-aire on for venting (turn off the dehumidifer part)
    @hvac-marc - Ultra-aire provided the HVAC contact which is same HVAC that installed the HVAC system when my house was built. There was no other HVAC installer available in my area for ultra-aire. Unfortunately this installer has never installed dehumidifier; this was their first one. Why I posted here wonder if install was right.
    Did you raise the dehu setting to 50%RH? does it shut off?
    Ideally to minimize the dehu run time raise the %RH control setting above the %RH that the a/c reaches during long runs. Again 50%RH is should prevent any adverse affect on the wood in your home. The Ultra-Aire dehu is designed to run 24/7.
    The picture is not clear on one point. Is the dehu supply connected to the a/c supply? It must be to get the full benefit of the dehu. I assume that you are able to maintain the low %RH but are running the dehu most of the time.
    As the outdoor dew points go below 50^F, the dehu will stop running. Idealling, you should figure out how the use the ERV for fresh air ventilation year around instead of the Ultra-Aire. Mainly because you have it and it will reduce the moisture load in the fresh air.
    Thanks again for helping us bring your a/c contractor up to speed on installation of dehumidifiers in quality homes.
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  8. #8
    Join Date
    Jul 2006
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by kdean1 View Post
    Is there a damper on the pipe for the bypass humidifier? It should be closed to prevent the air from the dehumidifier from circulating back through it.
    At the humidifier there's manual damper which I confirmed is closed.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •