+ Reply to Thread
Results 21 to 31 of 31
Thread: CVHE winding temp Alarm
  1. #21
    ottawa canada
    My money is on “someone left a rag in the motor cooling line”
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
  2. #22
    Aug 2018
    Columbus,Ohio
    Gas is coming out tomorrow ( hopefully ) I will update.
    Sent from my SM-G955U using Tapatalk
  3. #23
    The Hot South
    Which vintage machine is this? Which control panel? There have been issues with a bad crimp on the backside of the motor temp sensor terminal block which causes intermittent motor temp faults. If it’s AdaptiView, you can set it to ignore the first motor temp sensor fault and trip on the second motor temp fault. Or you could put a resistor on that sensor. Typically, if you have motor cooling issues, like a rag stuck in the machine, all of your sensors are going to read hot.
  4. #24
    Mar 2017
    Arizona
    What did you end up finding?
  5. #25
    Aug 2018
    Columbus,Ohio
    Found a piece of an old o ring.
  6. Likes ruuufuhbock liked this post.
  7. #26
    HEY! i didn't do it.
    "Right" is not the same as "Wise".
    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.
  8. Likes ruuufuhbock liked this post.
  9. #27
    ottawa canada
    Was there a rag wrapped around it to ?
    Wasnt me !!!!!
  10. Likes ruuufuhbock liked this post.
  11. #28
    Quote Originally Posted by Healey Nut View Post
    Was there a rag wrapped around it to?...
    You still can’t prove anything about that!
  12. #29
    Jan 2005
    Southwestern WI
    How did that get in there? That would not get through the refrigerant pump impeller.
  13. #30
    Aug 2018
    Columbus,Ohio
    Its a pre refrigerant pump model, the motor cooling line runs from the bottom of the condenser barrel to the motor and feeds off of differential pressure.
  14. #31
    ottawa canada
    My money is on someone didnt cover the ends of the open lines and when you were cleaning the O ring off either the discharge volute or the motor O ring a piece went in the motor cooling line .
    Always cover open ends with a rag and tape dont stuff rags down them as they get forgotten
  15. Likes ruuufuhbock liked this post.