    Hello

    I would like to take a test of the trane chiller
    I asked about how I could test gas for Chiller?

    Can I use the following data obtained from the controller to calculate subcooling or superheat:

    sat evap temp -Recognizes that the required difference is 5-8 degrees Celsius
    sat cond temp -Recognizes that the required difference is 3-7 degrees Celsius

    Why does the supplier give me these values ​​in the morning?

    I would appreciate your help

  2. #2
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,060
    Post Likes
    To calculate the SC and SH you need to know the pressure and convert to a saturated temperature then know the actual temperature the difference is the answer. Subcooling is condensor out and Superheat is evaporator out

  3. #3
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,060
    Post Likes
    don't see how this fits in industry news tough.