Thread: Trane chillers
    Jul 2016
    Trane chillers
    Hello
    I would like to take a test of the trane chiller
    I asked about how I could test gas for Chiller?
    Can I use the following data obtained from the controller to calculate subcooling or superheat:
    sat evap temp -Recognizes that the required difference is 5-8 degrees Celsius
    sat cond temp -Recognizes that the required difference is 3-7 degrees Celsius
    Why does the supplier give me these values ​​in the morning?
    I would appreciate your help
    Jan 2015
    Iowa
    To calculate the SC and SH you need to know the pressure and convert to a saturated temperature then know the actual temperature the difference is the answer. Subcooling is condensor out and Superheat is evaporator out
    Jan 2015
    Iowa
    don't see how this fits in industry news tough.