    Blown fuses of main incomer in turbocor compressor

    Today, I turned on 3phase supply to the turbocor compressor, at the same time, two fuses of the compressor found blown, The compressor first converts ac to dc, by the application of SCR, then stored to dc bus and then fed to motor through igbt, last time same fuses were blown out, but everything found ok, and machine too was working ok, What will be the reason behind the blown fuses?

    Sent from my TA-1004 using Tapatalk

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    16,998
    Post Likes
    Your turning on the main disconnect or starting the machine?

  3. Likes Ajit Lokhande liked this post
  4. #3
    Join Date
    Aug 2018
    Posts
    4
    Post Likes
    Thread Starter
    I just tuned on the supply, same time fuses blown out

    Sent from my TA-1004 using Tapatalk

  5. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    16,998
    Post Likes
    I would get someone with a Megger to test everything!