    It looks like its low on freon but it's not, cause the sightglass is clear liquid line not even warm.The compressor is pulling few amps below rated,there is something going on @ the condensor cause theres a lot of oil out my hose when I remove my gauges, I do want to mention that this is is 15ton split unit with 1 3/8 suction line may be it needs trap every 10ft & I dont see any,cause the roof is more then 50ft from the airhandler,am trying to give much as info I can.

  2. #15
    Join Date
    Aug 2014
    Posts
    226
    Post Likes
    Thread Starter
    theres a drier on liquid line outside the condensing unit.

  3. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,252
    Post Likes
    Measure the evaporator air flow!

    Measure the evap motor amperage!

    Do you fight to take the covers off?

    Comp oil sump hot, warm or cold?


    That System is OVERCHARGED

  4. Likes JeffWil liked this post.
  5. #17
    Join Date
    Aug 2014
    Posts
    226
    Post Likes
    Thread Starter
    I have measured the airflow, evap motor amp, not pulling enough amps, besides that I removed some freon as well,but still having issues.i need to find solution.the only thing that can cause restriction for the highside is the drier.

  6. #18
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,247
    Post Likes
    Is there a factory LLFD in the cond unit?

  7. #19
    Join Date
    Aug 2014
    Posts
    226
    Post Likes
    Thread Starter
    no, field installed only

  8. #20
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,252
    Post Likes
    Quote Originally Posted by nytech28 View Post
    I have measured the airflow, evap motor amp, not pulling enough amps, besides that I removed some freon as well,but still having issues.i need to find solution.the only thing that can cause restriction for the highside is the drier.
    Air Flow Issue!!!!!!!!!!!!!

    Someone or many have added refrigerant in an attempt to raise the suction.

    Pull the charge and weigh in a new charge.........

    Actually measure the air flow compared to the fan curve for the unit.

    Bet a fire damper(s) are closed!

  9. #21
    Join Date
    Aug 2014
    Posts
    226
    Post Likes
    Thread Starter
    waiting on customer,if he wants me to further proceed with the issue.

  10. #22
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,252
    Post Likes
    Quote Originally Posted by nytech28 View Post
    waiting on customer,if he wants me to further proceed with the issue.
    Another indicator i use is feel the oil sump.....If its cool or cold your slugging liquid!

  11. #23
    Join Date
    Aug 2014
    Location
    Hi, Usa
    Posts
    91
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Another indicator i use is feel the oil sump.....If its cool or cold your slugging liquid!
    Is this method works only when unit is running a while or could feel at startup to?

  12. #24
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,252
    Post Likes
    Quote Originally Posted by maint_rgh View Post
    Is this method works only when unit is running a while or could feel at startup to?
    While running.

    Just another Red Flag to look for!

  13. #25
    Join Date
    Aug 2014
    Posts
    226
    Post Likes
    Thread Starter
    I do feel foamy oil,on my guages,when removed.

  14. #26
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,252
    Post Likes
    Quote Originally Posted by nytech28 View Post
    I do feel foamy oil,on my guages,when removed.
    Thats why im asking what the temp of the oil..............

    Im confident theres a sever restriction of the air flow causing liquid slugging. That pulls the oil into the refrigerant stream and in-turn it goes all over more then normal!