    Email alarm to include value??

    I need to have the email body include the value of an out of range alarm extension. I have forgot how to do it? I have added to the email body to include. Value: %parent.out.value% which doesn't work. Any help would be appreciated.

  2. #2
    Join Date
    Jan 2003
    Location
    USA
    Posts
    5,197
    Post Likes
    Think the parent in that case is an alarm record not a point per say.

    %alarmData.sourceName% is currently %alarmData.alarmValue% and above the %alarmData.highLimit% alarm limit.
    %alarmData.sourceName% is currently %alarmData.alarmValue% and below the %alarmData.lowLimit% alarm limit.

    If you pull up an alarm in the console and double click on it to expand all the info, you can see where the above comes from. Anything in that record can be used in the email.
    Propagating the formula. http://www.noagendashow.com/

  3. #3
    Join Date
    Mar 2016
    Posts
    40
    Post Likes
    I found this list on Niagara Forums some years ago. I know it has helped me out.



    timestamp=Timestamp
    uuid=Uuid
    sourceState=Source State
    ackState=Ack State
    ackRequired=Ack Required
    source=Source
    alarmClass=Alarm Class
    priority=Priority
    normalTime=Normal Time
    ackTime=Ack Time
    user=User
    alarmData=Alarm Data
    alarmData.escalated=Escalated
    alarmData.msgText=Message Text
    alarmData.fromState=From State
    alarmData.toState=To State
    alarmData.notifyType=Notify Type
    alarmData.status=Status
    alarmData.newValue=New Value
    alarmData.setptValue=Set Point Value
    alarmData.errorLimit=Error Limit
    alarmData.deadband=Deadband
    alarmData.Count=Count
    alarmData.highLimit=High Limit
    alarmData.lowLimit=Low Limit
    alarmData.alarmValue=Alarm Value
    alarmData.offnormalValue=Offnormal Value
    alarmData.faultValue=Fault Value
    alarmData.presentValue=Present Value
    alarmData.numericValue=Numeric Value
    alarmData.feedbackValue=Feedback Value
    alarmData.feedbackNumeric=Feedback Numeric
    alarmData.controlledValue=Conrtolled Value
    alarmData.hyperlinkOrd=Hyperlink Ord
    alarmData.soundFile=Sound File
    alarmData.icon=Icon
    alarmData.sourceName=Source Name
    alarmData.notes=Notes
    alarmData.instructions=Instructions
    alarmData.TimeZone=Time Zone
    alarmTransition=Alarm Transition
    lastUpdate=Last Update

  4. #4
    Join Date
    Jul 2009
    Location
    Wa
    Posts
    442
    Post Likes
    Thread Starter
    Thanks guys for the input. Haven't had time to get back and test this again!! But I think you've cleared the fog for me. Thanks again.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR