+ Reply to Thread
Results 1 to 3 of 3

Thread: Trane chillers

  1. #1
    Join Date
    Jul 2016
    Posts
    6
    Post Likes

    Trane chillers

    Hello

    I would like to take a test of the trane chiller
    I asked about how I could test gas for Chiller?

    Can I use the following data obtained from the controller to calculate subcooling or superheat:

    sat evap temp -Recognizes that the required difference is 5-8 degrees Celsius
    sat cond temp -Recognizes that the required difference is 3-7 degrees Celsius

    Why does the supplier give me these values ​​in the morning?

    I would appreciate your help

  2. #2
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    To calculate the SC and SH you need to know the pressure and convert to a saturated temperature then know the actual temperature the difference is the answer. Subcooling is condensor out and Superheat is evaporator out

  3. #3
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    don't see how this fits in industry news tough.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •