    Customer requested the A/C Lines be reconnected ftom being cut and stolen prior to him purchasing the home for a flip house. Lines were tore off at and between the evap coil in the garage and the crawl space a couple walls over and down. System was left open. Work I did is shown prior to insulation on vapor line. I think it's pretty good for what I had to work with, and I feel good about the 30 cube drier I installed to help with moisture removal from the POE oil that's been exposed to air for about 4 months.
    Attached Images Attached Images    

  2. #2
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    Is that all hard copper? that's a lot of joints. I hope you used an oversized HH drier and some acid-away that's appropriate for the refrigerant used.
    Nest is POO!!

  3. Likes DavidDeBord liked this post.
  4. #3
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Thread Starter
    Yup hard Pipe, my preference, not seen much anymore tho. Yup 30cube HH drier. No acid away tho. (4) bends total on each line from evap to condenser be exact.

  5. #4
    Join Date
    May 2018
    Location
    Knoxville, TN
    Posts
    414
    Post Likes
    I prefer hard copper on anything 1 1/8" and bigger, normally use hard copper for the liquid lines as well if I use it for the suction lines. Just looks neater.

  6. Likes HVAC_Marc, DavidDeBord liked this post.
  7. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Hard copper I always use staybrite 8

    Half the heat and no need for Nitro purge

    Biggest pipe I ever see is 1 inch

  8. Likes DavidDeBord liked this post.
  9. #6
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    line set looks fine, condensate line not so much.

    done right = trap, then vent. should be ok though as its a positive pressure coil
    my boss thinks its possible to repeal the laws of physics

  10. #7
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Thread Starter
    Nothing else besides the line set is my work. The rest is existing done by someone else. Customer didn't want any of it changed.

  11. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Should have slipped the armor flex on while open!

    I prefer hard.....
    3/8 i would have used soft and a bender!

  12. #9
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Thread Starter
    Yes that's an easy way to do things, however I prefer doing it after the piping is complete and using a miter box with the arma flex to make perfect 90°s and seal it all really good. Again it's a style not seen much anymore but nonetheless one I prefer to use. As for the liquid line if I don't have to many bends I'll use the hard copper for it as well.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •