    I was just looking to provide the data plate info to see if I could do anything else but looks like I'll just have to wait til my co worker helps see if we can unclog the restriction.

    Thanks for the help will update this thread once it's been fixed.


    Sent from my iPhone using Tapatalk

  2. #28
    Join Date
    May 2006
    Location
    Deep Southeast
    Posts
    4,135
    Post Likes
    Quote Originally Posted by smokinaces View Post
    I was just looking to provide the data plate info to see if I could do anything else but looks like I'll just have to wait til my co worker helps see if we can unclog the restriction.

    Thanks for the help will update this thread once it's been fixed.


    Sent from my iPhone using Tapatalk
    You should first recover the 3lbs of refrigerant. If you put 10lbs in, it's way overcharged, thus the 450 psi head and compressor bypass (hiss).

  3. #29
    Join Date
    Sep 2011
    Posts
    25
    Post Likes
    Thread Starter
    Quote Originally Posted by vin lashon View Post
    You should first recover the 3lbs of refrigerant. If you put 10lbs in, it's way overcharged, thus the 450 psi head and compressor bypass (hiss).
    Will do thank you


    Sent from my iPhone using Tapatalk

  4. #30
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    847
    Post Likes
    I have enough difficultly looking up information for equipment I am working on, but that looks like the data tag for the outdoor unit and the furnace, what about the data tag for the evaporator coil ?

    if you are sure it is a piston you might need to up-size the piston to compensate for the long run ... double check airflow ( clean blower wheel / coil, duct work sizing and blower speed setting ) .....

    does look as if you are overcharged also ......
    he who wins is he who sits back and laughs at others who are stuck in their miserable lives

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.