    What would you do?

    Replace or add some solder and call it a day? Not even a pinhole leak.

    Sent from my LG-TP450 using Tapatalk

  2. #2
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    1,816
    Post Likes
    I guess it depends on the age. I'd ask the H/O. It might be the start of more to come. So let them know there options.
    Uh...Google it yourself!

  3. #3
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    20,923
    Post Likes
    If it's that black dot in the second picture, it looks like a pinhole to me. braze it over and call it good as long as the rest of the system is sound.