    compressor troubleshooting

    Hello,
    there is a 3 phase AC compressor, SR=0.9 ohm, SC=0.9 ohm, CR=0.8 ohm, i am not sure this compressor is short or not, someone said it should over 20000 ohm resistant, it is not ground.
    i have another single phase compressor shows: SR=0.7 ohm, SC=0.7 ohm, CR=0.8 ohm, it is not ground.
    can anyone tell me those two is good or not, thanks!

  2. #2
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    18,189
    Post Likes
    The three phase might be good, the single phase is not.
    If you were a real tech, you'd solder a relay on that board and call it good to go.

    I do a triple evac with nitro to remove non condensables.

  3. #3
    Join Date
    Aug 2016
    Location
    San Diego
    Posts
    186
    Post Likes
    On a three phase motor each reading should be about the same. So like BBeerme said the 3 phase motor is likely good. I'd replace the single phase one.

  4. #4
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    4,759
    Post Likes
    And the 3 phase is refereed to as L1-L2, L2-L3,, L1-L3.

  5. Likes DavidDeBord liked this post
  6. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    16,580
    Post Likes
    Post the Model #'s

    There generally listed on there sites.

  7. Likes DavidDeBord liked this post
  8. #6
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,892
    Post Likes
    From those numbers, I would say they are both 3 phase, and are good.

    You should Meg the windings to ground to be sure.

  9. #7
    Join Date
    Aug 2014
    Location
    Los Angeles
    Posts
    70
    Post Likes
    Thread Starter
    thanks for all replies! i have a fluke claim meter $150 only can measure <30 ohms resistant, but a $20 multi-meter can measure 15,000 bleed resistant, what is going on? for the small compressor(reception), it is easy to see over few ohms on CR,CS, RS, why the big scroll compressor has less 1 ohms on those terminal?