    I have an AX jace that's been there for several years. The input shows occupied but the output is unoccupied. If I change it it will start working, so it's like it is not retransmitting this value.


  2. #2
    Join Date
    Jun 2006
    Posts
    178
    Post Likes
    What control equipment do you have connected to the GCM? Do you have GCS’s or LCM’s or MZ2’s? If it’s really old you may have MZ1 and MF1 controllers and also is it a 84000 series or 86000 series GCM?

  3. #3
    Join Date
    Jun 2006
    Posts
    178
    Post Likes
    Also what driver are you using? Is it the original GCM driver that uses a serial cable between the GCM and Jace?

  4. #4
    Join Date
    Mar 2018
    Posts
    34
    Post Likes
    Thread Starter
    Unsure of drivers. It does serial in through a cable. I think I got it by setting the MaxSendTime to 5 minutes. I did that and waited and they cleared up.