    midwest
    compressor tt400 any idea on labor involved (hours roughly) to remove and replace an inverter on one of these machines. its on a McQuay wmc chille
    “The price of anything is the amount of life you exchange for it.” – Henry David Thoreau
    It's sad that we have become so accustomed to bad service that we're shocked when we get good service.
    Neil Cavuto
    Sep 2013
    Decant compressor, remove all top side bits, replace, vac, run and commission. Couple of hours. No more. Always been given a day to complete always seems about right. E
    Nov 2014
    Australia
    Yep, you'll be up & running in 8hrs... so long as it isn't a demagged shaft
    May 2009
    tropical paradise
    well, how long did it take on your first inverter swap? was that your only issue?
    Supernova86, you must be mr speedy. lol i'm more along the lines of ChillerR123 & 8 hrs. would be a piece of cake, if it wasn't on top of the chiller.
    ChillerR123, finally ran into the de-magnetized shaft... grr... through me for a loop for awhile & finally swapped the entire thing...
    The Hot South
    2 hours is pretty quick. You have to isolate the compressor and remove the charge. Then take all the topside components off. I’d say 8 hours for everything.