    Wood frame for evaporator coil support.

    We doubled the output of a 4 ton Ruud AC yesterday.

    A couple of years ago another company had replaced a condenser unit and evaporator coils in a manufactured home. They didn't, however, use matched equipment.

    The indoor coil was undersized for the outdoor unit. So, we replaced the evaporator coil with one that was properly sized.

    When we tested the original system the first time on an 80 degree day, it was only producing 24,120 Btu per hour.

    After our work, it was producing 41,764 Btu per hour on a 105 degree day!

    That is the kind of improvement that we like to see.

    Someone had also put a wood frame under the evaporator coil. Wood simply doesn't belong between the coil and the blower. The pictures show before and after views of that area. The black insulation is to prevent condensation from forming on the metal under the condensate tray. The brackets along the side keep the evaporator coil properly positioned over the opening to the blower compartment.
    Attached Images Attached Images   
    It's an upside down world we live in.

  2. Likes HVAC_Marc, kdean1 liked this post
  3. #2
    Join Date
    May 2006
    Posts
    3,190
    Post Likes
    whats with all the wire nuts ?

  4. #3
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    1,693
    Post Likes
    Thread Starter
    Quote Originally Posted by pctech View Post
    whats with all the wire nuts ?
    Thermostat wire connections to the heat pump condenser.
    It's an upside down world we live in.

  5. #4
    Join Date
    May 2006
    Posts
    3,190
    Post Likes
    I would have tried to put them inside some form of junction box makes it look so much neater

  6. #5
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    1,693
    Post Likes
    Thread Starter
    Quote Originally Posted by pctech View Post
    I would have tried to put them inside some form of junction box makes it look so much neater
    Agreed, just not enough time to fix everything.
    It's an upside down world we live in.

  7. #6
    Join Date
    Aug 2011
    Location
    Lewes, DE
    Posts
    999
    Post Likes
    thats literally how its supposed to be, you cant see the missing door.

  8. #7
    Join Date
    May 2006
    Posts
    3,190
    Post Likes
    you can tell it has a door but still the wireing would be redone if it was me doing the job and had the time i cant stand messy wireing