    Trane Odyssey Heat Pump

    After troubleshooting and finding a bad board and to verify I exchanged boards with a running unit and Condenser started up then after a few days unit stopped working. I did get a new board and still same problem. I have 24 volts to terminals on new board and I have checked High and Low pressure switches and getting continuity. I also have checked relays and continuity on normally closed. I do have high Voltage on terminal coming from disconnect to unit. Anything else anyone could suggest I check?

  2. #2
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    20,923
    Post Likes
    where does the high voltage stop?

  3. #3
    Join Date
    Jul 2009
    Location
    new york
    Posts
    812
    Post Likes
    Thread Starter
    High voltage stops where low voltage stops! The problem was unit was calling for Cooling but EZ trap was was open

  4. #4
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    20,923
    Post Likes
    well there you go then